[RE-wrenches] 120 Vac and 12Vdc mixed distribution system

John Blittersdorf john.blittersdorf at gmail.com
Wed Apr 24 08:00:37 EDT 2024


Jason,
  I have a customer with the same situation except he already has a 12 V
VFX inverter,  He has a sunfrost fridge and other small loads with a very
fancy custom control board
originally set up to handle AC and DC systems.  We are adding a lot more
solar and I was considering a dual battery system but the owner didn't like
that idea.  We are going with and Iota 12v power supply (i use one at my
house for my sunfrost) to power up all his DC loads and will be adding a
large 48 V battery bank and over 4Kw of solar using a VFXR3648 directly in
place of the 12V inverter.  He complained that the existing inverter would
not handle all his current AC loads very well.  My own house is fully wired
for 12VDC as well as AC (lots of #10 copper not being used) and I have been
considering getting a small LFP 12V battery to put back on by DC System.
Then use the Iota as a secondary charging method with some of my large
stash of older modules hooked up for 12V direct with C40 charge controller
to recreate my original system just for kicks. I'm only using DC for my
Sunfrost and one "emergency light" in the livingroom right now.  For your
customer, a small LFP 12v battery (approximately $500 or less) to replace
his old battery bankm and more larger ones for the new AC side with 48V
inverter fed by his generator or through an Iota 48 V charger ifusing a
smaller non charging inverter. Unlike Dave, I like these challenges. Maybe
thats why I never seem to make money.!!

John Blittersdorf
offgridvermont.com


On Wed, Apr 24, 2024 at 7:22 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Fortunately, the owner is pretty handy and is willing to live with any
> negative consequences. That said, I want to offer him something as simple
> and bulletproof as possible. I am walking into this with eyes wide open,
> for sure.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via
> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>> Not being helpful but I  walk away from these.  It will come back to you.
>>
>> *Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
>> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
>> text 209 813 0060*
>>
>>
>> On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
>>
>> I have an off-grid client who is working on replacing old equipment at a
>> cabin. He has a lot of 12 volt distribution in the house for lighting,
>> fans, and a 12 volt refrigerator. He also has 120 volt AC loads that run
>> through a separate distribution panel where the only source is a 2000 Watt
>> Honda generator. There is no inverter present. The batteries are charged
>> through a Trace C40.
>>
>> He currently has a few ancient solar panels and a struggling Bank of AGM
>> batteries. It's time for an upgrade. I can easily supply enough PV power
>> for what he needs. He currently has a 9 kilowatt hour battery capacity that
>> he was happy with when the batteries operated optimally. Nonetheless, I
>> would probably future-proof him with a 10 to 15 kilowatt hour LiPo to
>> double or triple his usable capacity.
>>
>> For convenience, obviously it would be nice to have an inverter to
>> eliminate or reduce the generator requirement. But he seems committed to
>> keeping his 12 volt distribution because it would be costly to replace
>> fixtures. I think he would consider replacing the 12 volt refrigerator if
>> he has an inverter.
>>
>> He definitely wants LiPo batteries.
>>
>> I don't like the idea of 12 volt direct from a battery plus connecting an
>> inverter to that same battery. It is going to be hard to measure and
>> monitor things.
>>
>> I am thinking about using a 48 volt battery with a single phase 120 volt
>> inverter, getting him to change to a 120 volt refrigerator, and using a DC
>> converter to give him somewhere in the range of 100 amps at 12 volts for
>> his existing DC lighting and fan loads. Is this a bad idea? Should I stick
>> with a 12 volt battery system? He does have a tiny 12 volt pressure pump
>> which might be an issue for the converter. I'm not sure. I am a bit worried
>> about the efficiency loss and capacity of DC converters and not sure how to
>> size it.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240424/c893967c/attachment.htm>


More information about the RE-Wrenches mailing list