On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
> I have an off-grid client who is working on replacing old equipment at
> a cabin. He has a lot of 12 volt distribution in the house for
> lighting, fans, and a 12 volt refrigerator. He also has 120 volt AC
> loads that run through a separate distribution panel where the only
> source is a 2000 Watt Honda generator. There is no inverter present.
> The batteries are charged through a Trace C40.
>
> He currently has a few ancient solar panels and a struggling Bank of
> AGM batteries. It's time for an upgrade. I can easily supply enough PV
> power for what he needs. He currently has a 9 kilowatt hour battery
> capacity that he was happy with when the batteries operated optimally.
> Nonetheless, I would probably future-proof him with a 10 to 15 kilowatt
> hour LiPo to double or triple his usable capacity.
>
> For convenience, obviously it would be nice to have an inverter to
> eliminate or reduce the generator requirement. But he seems committed
> to keeping his 12 volt distribution because it would be costly to
> replace fixtures. I think he would consider replacing the 12 volt
> refrigerator if he has an inverter.
>
> He definitely wants LiPo batteries.
>
> I don't like the idea of 12 volt direct from a battery plus connecting
> an inverter to that same battery. It is going to be hard to measure and
> monitor things.
>
> I am thinking about using a 48 volt battery with a single phase 120
> volt inverter, getting him to change to a 120 volt refrigerator, and
> using a DC converter to give him somewhere in the range of 100 amps at
> 12 volts for his existing DC lighting and fan loads. Is this a bad
> idea? Should I stick with a 12 volt battery system? He does have a tiny
> 12 volt pressure pump which might be an issue for the converter. I'm
> not sure. I am a bit worried about the efficiency loss and capacity of
> DC converters and not sure how to size it.
>
> Jason Szumlanski
> Florida Solar Design Group
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240423/b49813b5/attachment.htm>
More information about the RE-Wrenches
mailing list