[RE-wrenches] midnite new inverter
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Apr 10 13:55:22 EDT 2024
Hmmm. New world? It does have to run in the field reliably! Schneider
has had a 600v controller since 2012. It is all I use. Totally bullet
proof reliable. Attached specs.
Good Luck!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[8]https://offgridsolar1.com/ [9] [8]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2024-04-10 10:35 am, jay via RE-wrenches wrote:
> This is exactly the situation that the midnite AIO is addressing or
> similar.
>
> Lets say that you go with 11 panels ( and that works keeping it under
> 600voc).
>
> If you go with enphase, thats about $3000 with cable. Plus you'll need
> larger wire due to it only being 240vac vs closer to 380vdc for a DC
> series.
> That 600v controller will set you back between $1200-2000 with BOS and
> smaller wire.
>
> Using the $2000, and $3000.
> If the AIO is say $4500.
>
> Then for $2500 your getting 3 inputs, 600vdc, AFCI, and all the other
> bells and whistles. Much higher efficiency than AC coupling.
> And a 12 kw vs 8kw inverter.
>
> And if customer decides to go more solar, then the AIO is already set
> up to add more with $0 expense on the CC side.
>
> A whole new world
>
> Jay
>
> On Apr 10, 2024, at 11:06 AM, Maverick Brown via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Logan
>
> Is MidNite making the AIO or is it rebrand like the other guys?
>
> If MidNite is actually making it, that adds a whole new level of
> interest. MidNite makes great products already. This would be a game
> changer.
>
> Thank you,
>
> Maverick
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
> * Solar Commander Remote Power
> * SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
>
> On Apr 10, 2024, at 10:54 AM, William Bryce via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> All
>
> As a Beta tester and being a part of the development of the MNS All in
> One, MNS is working to ensure that the current limitations from the
> use of LA batteries will be addressed and supported.
>
> MNS is addressing the concerns of using an AOI inverter because failure
> will require the R&R of the unit. This AIO is designed to be completely
> field serviceable and MNS will stock the boards and will provide the
> technical help to get the system back up and running in the field.
>
> Thanks
>
> Logan
>
> On Wed, Apr 10, 2024 at 11:01 AM Steve Higgins via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
> Good Morning Wrenches...
>
> When it comes to lead batteries, just be cautious of the all-in-ones
> and some of the hybrid inverters.
>
> Most of these inverters were not designed for Lead batteries and will
> struggle to charge them, resulting in sulfation (undercharging) issues.
> Eventually, this will lead to swelling of VRLA or excessive gassing on
> Flooded Batteries. Unfortunately, many of the "Hybrid" or "All-in-One"
> inverters released in the past 5-8 years are tailored more to
> lithium-chemistry batteries. I can't tell you how many battery banks
> have been cooked over the past couple of years due to the inability to
> control charging settings.
>
> If you can't control the Bulk/Absorb Voltage and Time, as well as the
> end amps termination setpoints, you will generally struggle to get and
> keep a Lead-Acid battery charged regardless of the battery you are
> using.
>
> I looked at the Midnite site and I don't see a user manual yet, once
> it's posted I'll take a look and see if it's compatible for Rolls
> Batteries, I'm pretty sure it will as Midnight has been asking battery
> charging questions the last couple of years.
>
> [1]
> Steve Higgins ⋅ Technical Services Manager
> t +1.902.597.4020 m +1.206.790.5840
> f +1.902.597.8447 e steve at surrette.com
> [2] [3] [4] [5]
>
> -------------------------
>
> CONFIDENTIALITY: The information transmitted herein is intended only
> for the addressee and may contain confidential, proprietary and/or
> privileged material. Any unauthorized review, distribution or other use
> of or the taking of any action in reliance upon this information is
> prohibited. If you receive this email in error, please contact the
> sender and delete or destroy this message and all copies.
> -------------------------
>
> On Wed, Apr 10, 2024 at 7:29 AM jay via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
> Can you explain what changes the eg4 18 inverter has vs the Envy as to
> LA programming?
>
> To me the Envy has a big advantage due to it having AGS warm up/cool
> down that the EG4 does not.
>
> Jay
>
> On Apr 10, 2024, at 7:49 AM, Howie Michaelson via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> John,
> If you are thinking of pairing the Envy with lead-acid batteries, I
> would strongly suggest not doing it. Even though Fortress sales
> advertises the Envy to be compatible with lead-acid, after trying it in
> my off-grid home, I would emphatically say that it is not. The
> programming is inadequate, to put it kindly. And their support really
> doesn't have a clue about lead-acid - Fortress support literally said
> that they don't recommend pairing the Envy with l-a. However, I don't
> have an opinion about how it does with closed loop Li batteries.
> I did recently install an EG4 18k system, off-grid, with the client's
> knowledge that this was a bit of an experiment for me. Both the Envy
> and the EG4 are made by LuxPower and have been, to date, physically and
> programmatically almost identical. I had stayed away from EG4 since it
> seemed to be primarily aimed at the DIY market. However, the 18k
> appears to be a serious contender so far, although this installation is
> a fairly low stress situation. I've been fairly impressed with the
> system. While this 18k is paired with EG4 Lithium batteries, EG4 has
> been making adjustments to the firmware to make it much more friendly
> to lead-acid. If you decide to go this route, check with EG4 (installer
> support - ask for Jarrett or Colt) to see where they are at with
> upgrading the firmware.
> I am also eagerly awaiting Midnite's AIO entry...
>
> Howie
>
> On Wed, Apr 10, 2024 at 9:02 AM John Blittersdorf via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
> Time will tell where the failure modes are. I still don't like all
> the eggs in one basket. Do you have to send the units back for repair?
> Had enough of that with Trace SW series inverters..
> For off grid, I'll stick to the tried and true for now. For Grid tie
> it is just a financial hit. For off-grid power loss it is more
> important to deal with right away..
>
> I am going to try a Fortress Envy at my off grid home but will keep my
> Outback field repairable VFXR wired in just in case. I had a massive
> lightning strike between my house and a guest cabin 1/4 mile away and I
> lost power from my Fortress Eflex battery at the cabin and my Outback
> inverter at my house. I replaced the control board on my inverter ( I
> always keep one in reserve as it is usually the only board failure due
> to lightning) and was back on line in 1/2 hour and Fortress rushed me
> a new BMS board for the E-flex and a day later and a half hour swap had
> it back in service, Now it is a different story with 2 Simpliphi
> batteries I have from a customer that failed. I have to ship them to
> California to have them evaluated to see if we had damaged them by
> misuse. Lots of expense and time lost.
>
> John Blittersdorf
> CV Wind Service / Off Grid Vermont
> 802-770-8625
>
> On Tue, Apr 9, 2024 at 11:43 PM Scot Arey via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Wow, are we in the golden age of inverter/chargers? If it had 200-a.p
> pass thru it would be near perfect.
>
> Begs the question: are stand alone charge controllers becoming a
> historical artifact?
>
> Howard "Scot" Arey
> Owner, Solar CenTex
> 254-300-1228 _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org [6]
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org [7]
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org [6]
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org [7]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org [6]
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org [7]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org [6]
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org [7]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org [6]
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org [7]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://www.rollsbattery.com/
[2] http://www.facebook.com/RollsBattery
[3] https://www.youtube.com/RollsBatteryEngineering
[4] https://www.linkedin.com/company/rolls-battery-engineering
[5] http://www.instagram.com/RollsBattery
[6] http://re-wrenches.org/
[7] http://www.members.re-wrenches.org/
[8] http://members.sti.net/offgridsolar/
[9] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240410/6959eb4a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240410/6959eb4a/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: MPPT-100-600-and-MPPT-80-600-Datasheet.pdf
Type: application/pdf
Size: 238026 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240410/6959eb4a/attachment.pdf>
More information about the RE-Wrenches
mailing list