[RE-wrenches] Off-grid array far, far from the batteries

William Miller william at millersolar.com
Wed Apr 10 13:25:09 EDT 2024


Chris:

The Outback 100 amp controller operating at a max of 300 VDC might be a
good solution.

Pondering this further:  I suppose a 600 volt charge controller would be
better for voltage drop but I suspect one string of 12 would exceed 600
VDC. If true then strings of 6 would exceed 300vdc. If using a FM100 the
fall back is strings of 4. Strings of 6 into a 600 volt charge controller
is only marginally superior for voltage drop over strings of 4.

Using the nameplate wattage you are just over 100 amps at 48VDC satisfying
the power criteria.

An added benefit is that all of the electronics will communicate.

Recent pricing of the 100 seems to indicate the price has dropped
significantly making this a good value.

It is possible you could combine at the battery location and pull multiple
smaller conductors. You’d still need a disconnecting means at the array.
Run the numbers.

https://millersolar.com/MillerSolar/Resources/Voltage_Drop.xls

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Wed, Apr 10, 2024 at 9:41 AM Chris Daum via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

>
>
> The crazy things folks do.  Dear people:  We have a fellow who has an
> initial off-grid array with a Radian 8048A (and related e-panel, etc.) and
> six 410W Canadian solar modules.  He has six more of the same modules…but
> the ideal site for solar is 900 feet away from his batteries and the rest
> of the system.  Yeah, good planning, right?
>
>
>
> In terms of getting AC power out of his ‘new’ 6X array, Enphase won’t work
> since he doesn’t have an Enphase system.  We’re looking at perhaps SMA or
> Chilcon (so the size of the wire run won’t be so astronomical).  Any
> suggestions?
>
>
>
> Best,
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
> 406-777-4309 or 4321
>
> 406-777-4309 fax
>
> www.oasismontana.com
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240410/5739464b/attachment.htm>


More information about the RE-Wrenches mailing list