[RE-wrenches] midnite new inverter
John Blittersdorf
john.blittersdorf at gmail.com
Wed Apr 10 09:01:46 EDT 2024
Time will tell where the failure modes are. I still don't like all the
eggs in one basket. Do you have to send the units back for repair? Had
enough of that with Trace SW series inverters..
For off grid, I'll stick to the tried and true for now. For Grid tie it is
just a financial hit. For off-grid power loss it is more important to deal
with right away..
I am going to try a Fortress Envy at my off grid home but will keep my
Outback field repairable VFXR wired in just in case. I had a massive
lightning strike between my house and a guest cabin 1/4 mile away and I
lost power from my Fortress Eflex battery at the cabin and my Outback
inverter at my house. I replaced the control board on my inverter ( I
always keep one in reserve as it is usually the only board failure due to
lightning) and was back on line in 1/2 hour and Fortress rushed me a new
BMS board for the E-flex and a day later and a half hour swap had it back
in service, Now it is a different story with 2 Simpliphi batteries I have
from a customer that failed. I have to ship them to California to have
them evaluated to see if we had damaged them by misuse. Lots of expense
and time lost.
John Blittersdorf
CV Wind Service / Off Grid Vermont
802-770-8625
On Tue, Apr 9, 2024 at 11:43 PM Scot Arey via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Wow, are we in the golden age of inverter/chargers? If it had 200-a.p pass
> thru it would be near perfect.
>
> Begs the question: are stand alone charge controllers becoming a
> historical artifact?
>
> Howard "Scot" Arey
> Owner, Solar CenTex
> 254-300-1228
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240410/06f0df8c/attachment.htm>
More information about the RE-Wrenches
mailing list