[RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?

Ray Walters ray at solarray.com
Wed Mar 13 17:51:18 EDT 2024


I've gotten into discussions like this before with EEs.  They are not 
experts at what we do, and can get confused, and go down strange rabbit 
holes like the rest of us.  I agree with you that not switching the 
Neutrals is the way to go.  Its how we've always done it in most 
scenarios.  It only makes sense to have separately derived systems as he 
is advocating, if you were including a portable gen set input, since 
that gen set might have N-G bonded. Even if you separated the N-G bond 
on the portable generator, there's the chance they could connect up 
another generator later that was internally bonded.    None of this 
applies to your scenario from what you described, though.

The other problem I've had with EEs, is that once they make a decision, 
they don't really want to articulate the "Why" behind that decision.  
Very frustrating for the rest of us trying to understand and learn.  
I've asked for code references, etc. and they just have blown me off.  
Another reason I've moved away from consulting on larger projects.

I would take a look at 250.30, which says multiple parallel power 
sources should be treated as a single separately derived system. 
Exception 1 specifically says a single N-G bond is allowed for multiple 
power sources.

Ray Walters
Remote Solar

On 3/13/2024 3:19 PM, Mick Abraham via RE-wrenches wrote:
> Hi, Mechanix~
>
> My off grid project gig has redundant 120y208 generators that need a 
> 200a "break before make" manual transfer switch so the clients can 
> choose machine A or machine B. The switch has a lockable center-off 
> but I think the generators aren't set up for "lock out tag out". The 
> machines & the xfer switch will all be indoors and about 10 feet 
> apart. The AC power wires from each generator will be hard-wired to 
> the transfer switch & piped in EMT. I had planned for the transfer 
> switch to have a "solid neutral" bus bar (& I had planned to bond 
> Neutral to Ground in that box), but a consulting EE tells me the 
> neutral must be switched along with the three hots. The project is too 
> remote to have an AHJ, but the clients have requested a wet stamp from 
> the EE.
>
> I think his rationale is related to the N-G bond point location. When 
> I asked about his suggested location, the EE wrote: "The N-G bond will 
> be at each generator, so the neutral will be generated at the 
> generator providing power to the facilities."
>
> Mick resumes: The genset installation document says "The generator set 
> is shipped from the factory with the neutral and equipment ground not 
> bonded together." So...these gensets are not like those portables 
> where it's difficult to isolate the neutral. I've attached an image 
> that shows what the EE is advocating. The manual xfer switch that I 
> wish to use isn't made in "four poles" without going to the 400 amp 
> version and the 400a switch won't physically fit the available space.
>
> Can I make a credible case for the transfer switch being the "point of 
> first disconnect" instead of each generator taking turns at being the 
> POFD? If the transfer switch is also the bond point, can't the Neutral 
> from each generator happily meet at the neutral bus bar? OR: might the 
> EE have a concern about a loop (from the Neutral of one genset through 
> the bus bar then showing up on the terminal strip for the other 
> genset? Code citations would be appreciated along with your advice, 
> Wrenchies.
>
> During service intervals, both engines will be running for a 
> brief interval. Example: Gen A may be carrying the loads while the 
> mechanic manually runs Gen B as he completes an oil change. If I wire 
> it as the EE wishes, will both running machines play well safety-wise 
> if each genset has a N-G bond (with the equipment ground as their only 
> common connection)? How would the safety aspects change if both 
> machines are running but I've wired things per my original concept?
>
> Thanks as always, Mechanix. "The Wrench List is the Bomb!"
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com <http://www.abrahamsolar.com>
>
> Landline: 970-731-4675
> Cell phone or for text messaging: 970-946-6584
> ᐧ
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240313/0c2eef22/attachment.htm>


More information about the RE-Wrenches mailing list