Kirk,
That site looks specifically for the Envy inverters. Do you know if the
Guardian site is working? My credentials will not get me in at this time.
www.app.fortresspower.io
My sites have no comms between the batteries and the inverter, since it is
an Outback system.
And yes, there is certainly an issue with SOC drift over time without
getting a full charge. I was told by Fortress tech support that the eFlex
batteries needed to get over 55V to calibrate the SOC. Yet, in their
settings, the generator is only supposed to bring them to 54.4V. The solar
will bring it higher. But this was a problem here in upstate NY, where we
did not have a sunny enough day in the entire month of January.
Cheers,
Dave
On Thu, Feb 15, 2024 at 12:30 PM Dave Angelini Offgrid Solar via
RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> So this is all open loop with outback correct? I can't even get into
> Simplyphi. website today. Maybe the windows update...
>
> The battery below was suppose to be networkable but it looks like not much
> progress.
>
> - Model: AmpliPHI 3.8kWh
> - Inverter compatibility: Sol-Ark, SMA (coming soon), Schneider
> Electric (coming soon)
>
> A question, it looks like Outback is not closed loop with any battery
> company. I hope I am wrong!
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
>
> On 2024-02-15 8:57 am, Darryl Thayer via RE-wrenches wrote:
>
> Is it similar to my problem with my Simplify batteries? Over time, the BMS
> did not allow all cells to charge the same. To correct this, I had to
> charge each battery separately, and after this, they stayed equivalent for
> more years.
>
> On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Hi william
>
> Could you share the equipment used and what issues you had?
>
> Thx
> Jay
>
> On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Peter:
>
>
>
> I have only purchased one set of Fortress batteries. There have been
> issues, I am sure many of them self-induced. Fortress has been overall
> very responsive. There have been a few days where I could not get through
> to technical support but with persistence I always manage. Fortress has
> offered truck–roll compensation at a reasonable rate as well.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Peter Giroux via RE-wrenches
> *Sent:* Wednesday, February 14, 2024 6:47 AM
> *To:* 'RE-wrenches'
> *Cc:* pgiroux at mindspring.com
> *Subject:* [RE-wrenches] Fortress
>
>
>
> Good morning my fellow wrenchers. While I see the comments on SunPower and
> the challenges, are any of you having similar issues with Fortress? Their
> bms boards from the early classics have not held up and even after
> replacement there are still issues ( parallel batteries and stand alone not
> showing accurate #'s, ). While support has been, well supportive, the
> issues persist. Any thoughts or fixes you have come up with?? I just had a
> customer unplug the coms cable from their sol-ark and bring their readings
> to volts VS %% and it is starting to work a bit better. Any and all help or
> ideas appreciated.
>
>
>
> Thx
> peter Giroux
>
> American Solar
>
> Norcross Ga
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
[image: Logo] <https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com <http://www.sungineersolar.com/>
c: (607) 270-0370
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240215/449baa71/attachment.htm>
More information about the RE-Wrenches
mailing list