We generally avoided using the 41 series inverter for reasons specified here
<https://millersolar.com/MillerSolar/case_studies/SMA_40_Series/Whats_wrong_with_40_Series.html>.
If you find a new string inverter in the SMA lineup, you might want to
check to see if they have resolved some of the shortcomings.



I have not had reason to use string inverters because, other than Solar
Edge, they do not offer intrinsic rapid shutdown.  Careful reading of the
NEC indicates that even ground mount arrays require RSS unless the PV
feeders run to a building with the sole use being to house solar
equipment.  Having said that, I would imagine that if an inverter were
mounted on the ground-mount rack, the requirement for RSS could be avoided.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Jeremy Rodriguez via RE-wrenches
Sent: Monday, January 8, 2024 1:44 PM
To: re-wrenches at lists.re-wrenches.org
Cc: Jeremy Rodriguez
Subject: [RE-wrenches] SMA String inverters



What are you wrenches that used to install the SBXXXX-41 units sourcing
now? Looks like there is a new model on their website





Jeremy Rodriguez

Solar Installation / Design

All Solar, Inc.

1453 M St.

Penrose Colorado 81240



Sent by Jeremy's iPhone. Sorry for typos and shorthand.

_______________________________________________

List sponsored by Redwood Alliance



Pay optional member dues here: http://re-wrenches.org



List Address: RE-wrenches at lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



There are two list archives for searching. When one doesn't work, try the
other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

http://www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20240110/8f09f6fc/attachment.htm>


More information about the RE-Wrenches mailing list