Drake,
Look up Stego snap-action t-stats at
automationdirect.com.
[image: image.png]
They are offered in NO or NC versions. contacts rated for up to 30W @ 24-72
vdc. Din rail mountable, $21 ea.
On Wed, Dec 13, 2023 at 11:08 AM Drake Chamberlin via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hello,
>
> Does anyone know of a 48 VDC temperature sensing relay? I need to use one
> to control a fan in a 48 V battery bank, to bring in cold air when the bank
> gets too hot from the wood heating system in the house.
>
> The relay needs to operate with the 48 VDC power supply and disconnect a
> small current with 48 VDC contacts.
>
> Thank you,
>
> Drake
>
>
> *Drake Chamberlin*
>
> *Athens Electric LLC*
>
> *Ohio Electrical Contractor’s License 44810*
>
> *NABCEP Certified PV Installation Professional*
>
>
> --
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 33st Anniversary 1991-2024!!*
dba Vermont Solar Engineering
802.559.1225
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231213/2a8cb9fd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 242845 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231213/2a8cb9fd/attachment.png>
More information about the RE-Wrenches
mailing list