[RE-wrenches] XW Drop in replacement inverter
Kevin Pegg
kpegg at energyalternatives.ca
Wed Oct 25 14:57:23 EDT 2023
Physically it is all the same. Software is way more complex. As Dave mentioned, you have to follow the commissioning process.
AC1 will no longer accept generator input, it’s grid-only now. So if you have a genset you will need to move that to AC2. This is one of the most irritating changes with the XWPro. Makes dual-generator configs a lot more complex now.
Kevin
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Chad Waits via RE-wrenches
Sent: October-24-23 2:18 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Chad Waits <chadwaits at netzerosolar.net>
Subject: [RE-wrenches] XW Drop in replacement inverter
Wrenches,
We have a client that had us construct a solar trailer for them back in 2014-2015 timeframe. The Current XW6048-120/240-60 is cooked and I'm wondering if the Schneider rep (or you savvy off grid guys) on here could tell me if the newer XW Pro 6.8kW 120/240 is an exact drop in replacement for a system including the the old power distribution panel accessories.
Thanks!
Chad Waits
President - Net Zero Solar
945 W. Silverlake Rd, Tucson AZ 85713