[RE-wrenches] Line Side Tap

Christopher Warfel cwarfel at entech-engineering.com
Fri Oct 13 16:51:33 EDT 2023


The intent of the line side tap, was to allow larger pv systems to 
interconnect to the SE conductors and not have to consider the service 
panel. So, I agree with others that the service panel has no 
consideration for what you are doing. The panel is protected by the MSP 
Breaker.  Chris

On 10/12/2023 8:06 PM, Drake Chamberlin via RE-wrenches wrote:
> We have a design where the conductors will come out of a 400 A meter 
> base to a junction box. Splices in the box will allow for the PV to 
> feed the meter.
> A maximum of 312 Amps can come from the inverters to feed the grid.
>
> The loads on the existing main service are significantly less than 
> 200A. The service is rated at 200 A, 3 phase delta.
>
>
>
> The conductors from the meter would be rated at 400 A to the splice, 
> as would the conductors to the photovoltaic system. The conductors to 
> the existing service would be downsized to 200 A.
>
> We were told that the bus bar rating of the service must also be 400 
> A, even though the output of the PV does not feed through that box. Is 
> there a rule that says this? What would be the logic?
> Thank you,
> Drake
>
> /Drake Chamberlin/
>
> /Athens Electric LLC/
>
> /Ohio Electrical Contractor’s License 44810/
>
> /NABCEP Certified PV Installation Professional/
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231013/5599ee22/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 69a02214.png
Type: image/png
Size: 48188 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231013/5599ee22/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231013/5599ee22/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/vcard
Size: 203 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20231013/5599ee22/attachment.vcf>


More information about the RE-Wrenches mailing list