[RE-wrenches] Generator question

Darryl Thayer darylsolar1 at gmail.com
Mon Sep 25 12:34:47 EDT 2023


Generators are load responsive.  They can not be back feed, one approach is
to take heavy loads and have the inverter drop these loading heav load
situations.  bring these loads on line with a PLC

On Mon, Sep 25, 2023 at 11:22 AM Chris Daum via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

>      Hi folks:
>
>
>
> We have a situation where the Sol-Ark 12kW Inverter isn’t able to
> adequately manage the loads and perform auto-gen start other than low
> battery level.   And despite thorough understanding of the customer’s
> initial loads, after he’s bought the system, he’s continued to add more and
> more loads – a severe case of load creep.
>
>
>
> He’s got a 38KW generator and we’re looking for the components to make the
> generator *load responsive* instead of just kicking on when the battery
> voltage is low.  Are there any ideas on switching equipment that can do
> this and work with the Sol-Ark?  We’re waiting for a reply from Sol-Ark,
> but thought you folks may have some ideas.
>
>
>
> The original design was for a larger solar system and inverter, but the
> customer balked at the cost and said he’d reduce his loads accordingly.  Unfortunately,
> that has not happened!   Now we’re trying to bend the laws of physics and
> have his 38KW  generator make up the difference. We need to come up with
> a means of accommodating the compromised design and now are faced with
> additional loads -- along with a significantly reduced solar array.   Is
> there a way to make this (2 wire start) generator more load responsive?
>
>
>
> Thanks for any and all advice!
>
>
>
>      Chris Daum
>
>      Oasis Montana Inc.
>
>      406-777-4309 or 4321
>
>      www.oasismontana.com
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230925/ce0ebabb/attachment.htm>


More information about the RE-Wrenches mailing list