[RE-wrenches] Sunny Island/Fortress E-vault

William Miller william at millersolar.com
Tue Sep 19 15:39:52 EDT 2023


Kieran:

I have read the documentation. Fortress tech support said there have been
problems and recommended open loop.

Do you know what parameters are passed with closed loop?

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Tue, Sep 19, 2023 at 12:18 PM Kienan Maxfield via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> That's actually incorrect, Fortress totally does support closed-loop with
> the SMA Sunny Island inverters. Here is their integration guide. This has
> all of the instructions and coms wiring, etc. -
> https://learn.fortresspower.com/external/manual/sma/article/introduction-useful-links?p=dc8b9a9c1b3f410556835193e66f2257c662403dfb3da4056e618e954e8381d2
>
> Thanks,
>
> Kienan Maxfield
> Technical sales, Technical Support
>
> *Green-Go Solar Distribution*
> *kienan at dist.solar* <https://kienan@dist.solar/>
> *(801) 631-5584 (Cell)*
> *www.distribution.solar <https://www.distribution.solar/>*
>
>
>
> ------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf
> of Kirk Herander via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent:* Saturday, September 16, 2023 8:33 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Kirk Herander <kirkh at vermont.solar>
> *Subject:* Re: [RE-wrenches] Sunny Island/Fortress E-vault
>
> Jerry,
>
> Who is the maker of the Blue Planet/Outback SOC box interface you mention?
>
> On Sat, Sep 16, 2023 at 9:30 AM Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Mac, wrenches
> SMA and fortress can only open loop and with a fixed temp sender its fine.
> Now on the blue planet and open loop with outback, you need a SOC box that
> they can make for you, it will interface with the blue planet and command
> the genny.
> Fun times
>
> On Sat, Sep 16, 2023, 6:04 AM Mac Lewis <maclewis1 at gmail.com> wrote:
>
> Hi William,
>
> Are you doing open loop or closed loop communication?  I'm not sure if
> Fortress can do a closed loop with SMA or not.
>
> We struggled to get the open loop to work well with some Blue Ion
> batteries, not from a charging sense but from a sense of getting the auto
> gen start to trigger correctly.  Basically, the SOC algorithm was always
> way off.  For a while we were using an external voltage trigger and we
> could get the generator to start OK before BMS shutdown.  We have since
> added a Namaka box and are using the "Ext BMS" setting for battery type in
> the Sunny Island and it has been working very well.
>
> I think the difficulty arises because the Sunny Island is so
> State-of-Charge centric and you can't manipulate the SOC algorithm without
> that Ext-BMS setting (and solid communication).  One weakness of the
> ext BMS setting is that it won't fall back on Voltage settings if battery
> communication goes down, but this is a weakness throughout closed loop
> communication for many manufacturers.
>
> Let us know if there is a Fortress to SMA communication solution.
>
>
>
>
>
> On Fri, Sep 15, 2023 at 11:11 PM Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> William, Wrenches
> Yes I do and it does require some basic electronics to make it work
> correctly, you will need to remove the ttemp sender and make a
> resistor pack to simulate the 77 degree reading otherwise it will not
> charge properly, for the first one I used a breadboard to set the temp for
> what I wanted to see then build a more solid state shrink wrap resistor.
> Doing this will prevent undercharge by the SMA and your customer will be
> happy to see the full state of charge at the batteries.
> OldSchool fun times
>
>
>
> On Thu, Sep 14, 2023 at 2:12 PM William Miller via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Friends:
>
>
>
> I am commissioning an E-vault battery array to an existing SMA Sunny
> Island System.  Does anyone have any experience with this they could share?
>
>
>
> Thanks.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> --
>
>
>
> Mac Lewis
>
> * "Yo solo sé que no sé nada." -Sócrates *
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230919/f15314ee/attachment.htm>


More information about the RE-Wrenches mailing list