[RE-wrenches] GT w/ BB
Michael Morningstar
mjmorningstar at gmail.com
Mon Sep 18 19:15:11 EDT 2023
I've been making gutter bus wireways that run the length of batteries and
inverters allowing for exact lengths of cables. I think I posted a picture
of an exceptionally large one. 24' long. I'm looking at the rack mounted
set up because the bussing and cabling is done. 3 racks of 6 5kwhr
batteries. All I will need is cabling from the racks to a small (in size)
bussbar
On Mon, Sep 18, 2023 at 3:50 PM Jay <jay.peltz at gmail.com> wrote:
> Sounds like a good design.
>
>
> As a tangent question to 13 parallel batteries, such as you’ll need
> Michael.
>
> How are people wiring larger numbers of lithium batteries together in
> parallel?
>
> Massive buss bars which I’m not sure how to do in a code compliance way.
> Or
> Not worrying about different cable lengths?
> Or
> Adding another conductor to the farthest batteries to compensate for VD
> Or
> Making all the cables the same length?
>
> Thx
>
> Jay
>
>
>
>
>
>
>
>
>
>
>
>
> On Sep 18, 2023, at 4:37 PM, Michael Morningstar via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Jay,
> I'd like to design for 60kw supply and 100kWh battery. I think I'm going
> to try the Discover rack mount set up rather than AES's and custom bussing.
> Jason,
> That's exactly what I was thinking, if I go the Sol-Ark route. Last time I
> ordered custom panelboards like that, they were six months out.
>
>
> On Mon, Sep 18, 2023 at 1:18 PM Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> If 40kw is the peak and then there are new added loads, what 50-60kw?
>>
>> If it was me I’d be designing the inverters to handle the 50/60 kw with
>> future expansion capabilities beyond that.
>>
>> Then how much kWh of storage are you going to need or maybe are planning
>> for?
>>
>> At some point maybe looking at a larger single inverter with high voltage
>> battery vs 48v?
>> I’m not sure if there are any 120/240 versions yet.
>>
>> Jay
>>
>>
>>
>>
>>
>> On Sep 18, 2023, at 12:36 PM, Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>
>> I like the Sol-Ark idea having had a few dual-unit successes recently. In
>> terms of combining them, the Sol-ark manual has a good triple unit wiring
>> diagram on page 53. You would have to use two 400A panelboards with three
>> 200A breakers for each to follow this diagram. However, I don't see the
>> point of a combining load center on the load side of the paralleled units.
>> The Sol-Arks each have a 200A integrated load breaker, so why not just
>> combine the outputs in a multi-tap connector or busbar? I think there is a
>> code-compliant way to make that work, but I haven't studied it with three
>> units.
>>
>> I would definitely ditch the SolarEdge inverters and just make it DC
>> coupled to the Sol-Arks. You don't need these to be a failure point in the
>> system, and the AC coupling will reduce the energy production in backup
>> scenarios.
>>
>> It sounds like you would have to get the six 200 feeders out of the
>> meter/main and into a new panelboard on the load side of the Sol-Arks. So
>> that's another required load center.
>>
>> And if money is truly no object, I would consider a manual transfer
>> switch to bypass the inverters for service. I'm afraid to look up what a
>> 400A DPDT switch costs.
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>>
>> On Mon, Sep 18, 2023 at 1:14 PM Michael Morningstar via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> I've been asked to build a back up system for a grid connected estate.
>>> We haven't done many of these and I thought it best to ask those who have
>>> some questions before I go about reinventing the wheel.
>>>
>>> Here's the existing infrastructure.
>>> 1) 400amp Metered Main Distribution Panel with six 200amp feeders to
>>> various sub-panels on the property
>>> 2) 400amp ATS and 100kw Kohler rapid response generator
>>> 3) 20kw ground mount array with (2) SE Inverters located at the array.
>>> Feeder from array is 1,000 ft to Service. Six years old and wiring is janky.
>>> 4) Data logging for the last year shows peak demands of almost 40kw.
>>> This could increase as several of formerly vacant guest residences could
>>> be occupied.
>>>
>>> My go to is almost always Schneider, however in this instance when I
>>> looked into a quad stack, or more It seems like some type of controller is
>>> needed to prevent imbalanced current passing through the relays during
>>> transfer. That left me a bit concerned. Has anyone successfully stacked 4
>>> or more XWPROs?
>>>
>>> Then there is the matter of AC or DC coupling? I really want no part in
>>> having anything to do with SE. The inverters are already looking pretty
>>> weathered taking the brunt of the prevailing winds and storms (they are
>>> mounted to one of the ground mount poles). Seems like a great waste to pull
>>> out the 4/0 feeders and replace strings. My other hesitancy with AC
>>> coupling is that we would lose PV monitoring and control.
>>>
>>> I've also considered Sol Ark 15's, like three of them. We've got some SA
>>> systems under are belt now and the only thing I can say that I like is the
>>> speed of installation and the 200amp pass through. Other than that, they
>>> leave me uninspired. One very large system continues to have glitches that
>>> SA just shrugs their shoulders about. If we were to do three 15's, *what's
>>> the preferred combining method?* All that I can come up with is a
>>> custom 400a panelboard w/ three 200a breakers.
>>>
>>> Price is not a consideration for this project. The new owners of this
>>> property (which is plagued with outages) have tasked me with building
>>> something that is ultra reliable and good take over in a situation where
>>> the grid is no longer available.
>>>
>>> Any suggestions or tips are appreciated.
>>>
>>> Michael
>>>
>>> --
>>>
>>> Michael Morningstar
>>>
>>>
>>> Morningstar Electric
>>>
>>> PO Box 1494
>>>
>>> Mount Shasta, CA 96067
>>>
>>> 530-921-0560
>>>
>>> mjmorningstar at gmail.com
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
> Michael Morningstar
>
>
> Morningstar Electric
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> mjmorningstar at gmail.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael Morningstar
Morningstar Electric
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230918/4fcaf767/attachment.htm>
More information about the RE-Wrenches
mailing list