I just replaced two Sunny Islands and one Sunny Boy that I did not install
with a single Sol-Ark 15k today. The generator installer (not me) had
already installed a custom but simple time delay relay. I didn't get into
the logic of it, but from what I understand the generator already had a
cool-down period when remote start signal is lost, but no warm up delay.
Major deficiency? I think that is actually pretty accurate and Sol-Ark
should fix it, but it isn't too hard to take care of it another way.
I wonder if this has something with the distinction of accepting generator
input on the grid input as well. You would not want a grid delay if it were
a utility. Still, they should be able to build in that logic I would think.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
On Fri, Sep 15, 2023 at 8:28 AM Michael Morningstar via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> We learned of this major deficiency after an eight unit install. No cool
> down is disastrous to modern diesels. Our work around was installing a
> 400amp contactor and macromatic programmable relay.
>
> On Thu, Sep 14, 2023 at 10:05 PM Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Jay, wrenches
>> ASCO makes multiple ATS controls that can manage delays latching up and
>> for cool down. Most of the gensets have are programmed cool down after
>> relay opens so its not an issue. Generally on start up the genny connects
>> as soon as it's voltage and freq are within range.
>> fun times
>>
>>
>>
>> On Thu, Sep 14, 2023, 2:26 PM jay via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hi All,
>>>
>>> I have a client with a sol ark and it doesn’t have warm up or cool down,
>>> kind of amazing companies are going backwards in their tech.
>>>
>>>
>>> Has anyone come up with external fix for this?
>>>
>>> I am guessing the internal relay on the sol ark switches closed when it
>>> sees the correct volts/hz and opens the sol ark relay when it sends the off
>>> signal.
>>>
>>> If thats correct I can pretty easily use a delay relay on the off cycle
>>> assuming the on signal has a time window to allow for this delay in sending
>>> power to the inverter.
>>>
>>> The on delay I don’t see anyway unless I use a contactor with on delay
>>> relay.
>>>
>>> Maybe there is a off the shelf generator transfer switch that has this
>>> built in?
>>>
>>> Thanks in advance
>>>
>>> Jay
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
> Michael Morningstar
>
>
> Morningstar Electric
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> mjmorningstar at gmail.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230915/89876b00/attachment.htm>
More information about the RE-Wrenches