[RE-wrenches] Sol-Ark 15k Conduit Entries
Lou Russo
russo.lou at gmail.com
Thu Aug 3 18:39:59 EDT 2023
Hello All,
Super impressive install, Michael. Almost worth a flight, and a site visit!
Back to Jason's initial question....
If you are using the 15kW Outdoor Sol-Ark they vent from the top and bottom
with a required 6" minimum spacing on both the top and bottom.
A 12kW Outdoor with 8x8 gutter and 1" offset nipples have worked great for
us.
Aloha,
Lou Russo
(808) 345 6762
On Thu, Aug 3, 2023 at 7:09 AM Michael Morningstar via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Drake,
> Those are single phase combiner panels. I would have loved to set this up
> as a three phase system, but there was already a mile of underground single
> phase run throughout the property. We ended up running a half mile 15KV
> line from the power site to the estate. This is an aside, it's kind of hard
> to see, but for seperation, we attached the pv circuits to the back of the
> gutter using through bolted adhesive backed cable tie holders. Often we use
> gutter dividers. They originate in the tall cabinet at the end which houses
> controls, secondary PV disconnects, AC and DC egauges, Tigo hub, Battery
> hub and (Lynk II). On the opposite end is a similar cabinet for the
> collection and distribution of AC circuits. Also, above and below the
> batteries are small gutters for communications and CT wires that run from
> the transfer switches to eguage. One transfer switch to alternate usage
> (alternating relay) or bypass between Gen 1 and Gen 2, and the other switch
> to select inverter or generator power, locally or remotely. In the AC
> cabinet there is a 400a contactor and time delay relay to achieve a
> generator cooldown as the janky Sol-Arks don't do that and it's hell on new
> diesels not to have that function.
>
> On Thu, Aug 3, 2023 at 7:50 AM Drake Chamberlin via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> That looks really nice. How were you able to put 8 Sol Arc inverters on a
>> 3 phase panel? Tech support told me that inverters had to be connected in
>> groups of 3.
>>
>> Thank you,
>>
>> Drake
>>
>>
>> *Drake Chamberlin*
>>
>> *Athens Electric LLC*
>>
>> *Ohio Electrical Contractor’s License 44810*
>>
>> *CO Master Electrician’s License 4526*
>>
>> *NABCEP Certified PV Installation Professional*
>> ---
>>
>>
>>
>> On 2023-08-02 14:19, Michael Morningstar via RE-wrenches wrote:
>>
>> 10x10 gutter. Notice within, a 2.5x2.5 gutter for comms. 1 x 2.5" nipples
>> work well. Chase nipples wont due to door clearance. I've also cut the
>> bottoms out of the Sol-Arks and a corresponding square window in the
>> gutter, placed a 1/4" rubber gasket between the two. We do that when we
>> have many VFD's over a gutter. Someone a while ago asked for a picture
>> showing how we make long bussbars. This one is 24' long.
>>
>> On Wed, Aug 2, 2023 at 10:08 AM Jerry Shafer via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Jason
>> In plenty of applications l will use couplers with chase nipples, height
>> is one issue but installed working height is very important. I use a 8"x8"x
>> X gutter and sometimes even off set that from the wall, l have had AHJ not
>> want to see mixed cables LVDC and AC in the same conduit so pass through
>> the battery conductors right out the bottom and to the battery. I just
>> create a template for punching into the gutter, looks clean and is safe
>> with easy access to the display
>> Fun times
>>
>> On Wed, Aug 2, 2023, 8:04 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>> I see a lot of pictures with conduit nipples coming out of a gutter that
>> are fairly long. I have a height limit issue and I'm wondering if there are
>> any negative implications of using very short nipples between a wireway
>> below and the inverter. I'm thinking about using close nipples or perhaps
>> 2-in nipples if I have enough room.
>>
>> If there are any practical reasons that this will not work well, please
>> let me know.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>>
>> --
>>
>>
>>
>> Michael Morningstar
>>
>>
>>
>> Morningstar Electric
>>
>> PO Box 1494
>>
>> Mount Shasta, CA 96067
>>
>> 530-921-0560
>>
>> mjmorningstar at gmail.com
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
> Michael Morningstar
>
>
> Morningstar Electric
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> mjmorningstar at gmail.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230803/921238f6/attachment.htm>
More information about the RE-Wrenches