Are we all thinking single phase? Another idea would be to use plastic
enclosures in at least some way to break the magnetic path. This is a lot
of current, and it will cause magnetic heating where the magnetic loop is
complete.
On Thu, Jun 29, 2023 at 10:19 AM Kirk Herander via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> All,
>
> I am in the middle of commissioning a 480kwh BP LFP battery bank,
> connected to -10- OB Radian 8kw inverter/chargers.
>
> For the DC combiner I am using midnite 2000 amp combiner boxes, modified
> to mount class T fuses on the positive bus, for both battery inputs and
> inverter outputs.
>
> For starters, I set the master inverter at a max charge rate of 20 AC
> amps, which equates to a DC charge of about 74 A. All the other inverters
> are automatically set to this charge rate as well.
>
> Turning the chargers on one by one, I started to get quite an audible
> vibration from the combiner box at a combined charge of about 400 to 500 A.
>
> So I took the cover off of the combiner, which was vibrating noticabllly
> by feel. Most of the noise was from the cover not fitting tight. But the
> The box itself is also vibrating by feel.
>
> I took the combined charge up to 640A dc. This level of vibration
> definitely increases with an increased charge rate. And I am surprised
> because after all, we’re not talking AC here we’re talking DC. It almost
> reminds me of a large AC transformer in its behavior. The vibration did not
> seem to be originating at the inverters, then resonating to the combiner.
>
> I can dampen the vibration by adding a few things, but I’m surprised that
> this is happening. All connections in the combiner are tightened properly.
> Ideas?
>
>
>
>
>
>
>
>
>
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 32st Anniversary 1991-2023!!*
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230630/2caabd1c/attachment.htm>
More information about the RE-Wrenches
mailing list