[RE-wrenches] Low Frequency transformer off-grid inverter options
Christopher Warfel
cwarfel at entech-engineering.com
Fri Jan 13 13:52:18 EST 2023
Have they already installed soft starts on these motors? Chris
On 1/13/2023 1:41 PM, Starlight via RE-wrenches wrote:
> Mac,
>
> What was the lowest voltage measured at inverter battery terminals
> during the inrush measurement?
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hello Wrenches,
>
> I have a new client that has ran a pretty decent wood shop for about
> 10 years on a Magnum 4448. He's got some large loads, planers, saws,
> compressors vacuums etc. They are really nice, heavy duty pieces of
> equipment. Amazingly, the Magnum has been able to start these loads
> for the most part for 10 years, but he has reported that it has gotten
> worse lately (could be a load issue), brown outs, dimming etc
>
> He wants to upgrade the system, get remote monitoring etc. I tried a
> test with a Sol-Ark 12, and it won't start these large motor loads. I
> was a little surprised by that but I know they aren't as good as the
> low freq transformer based inverters at these surges.
>
> I confirmed that its not just an overload from imbalance because the
> 240V loads will also overload it. I got an inrush measurement of
> 48.5A Ac @240 (but it didn't start the load before Sol-Ark would shut
> off)
>
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
>
> Any others I should consider? He does have some significant 120 only
> loads so I don't think the Outback vfxr are a good choice.
>
> Is it as simple as saying if the Magnum can start this load, the
> Radian should?
>
> I appreciate your input!
>
> --
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
>
> *
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230113/0eb7fd1b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230113/0eb7fd1b/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/vcard
Size: 203 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20230113/0eb7fd1b/attachment.vcf>
More information about the RE-Wrenches
mailing list