Hey All a Cheery Season to you all!
I inherited a backup system that had "failed". It was unwired, & poorly
labeled.
1200 AHR AGM Battery - 1 Radian 8KW inverter - 200 amp Generac transfer
switch - No solar - Feeding a 200 amp house panel.
First I explained the there were too many loads for an 8KW inverter. It
could & may overload the 8KW inverter. They said "it had worked fine for 5
years & they were OK with it as is please get it back up".
Replaced the existing Eaton transfer switch as the Generac controller was
shot, with a Generac 200 amp Xfer switch complete with controller & transfer
switch.
Rewired & had to recharge the 48 volt battery from 20volt back up to full
with a pair of IOTA chargers in series.
The original trigger was 3 wires from the Radian to the 12 volt & AUX output
to the input on the Generac controller. These were disconnected on the
Generac end. So no clue or labeling there.
I called Outback & they called it Redneck engineering & send me a few
articles to read.
Has anyone configured a backup in this manner?
All suggestions appreciated, thanks & wishing you all a safe & sane season!
Dana Orzel Great Solar Works, Inc.
C - 208.721.7003 dana at solarwork.com
Idaho Contractor - # 028765 Idaho PV # 028374
www.greatsolarworks.com <http://www.greatsolarworks.com/>
www.solarwor.com <http://www.solarwor.com>
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20221217/e9017462/attachment.htm>
More information about the RE-Wrenches
mailing list