My bet is on a neutral to ground bond inside the generator!

Roy Butler
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747www.four-winds-energy.com

Education is when you read the fine print; experience is what you get when you don’t.

“The less people know, the more stubbornly they know it.”

Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.

                 

On 12/16/2022 1:35 PM, Kirk Herander via RE-wrenches wrote:
> You may have neutral and ground connected at more than 1 location, 
> meaning at the genset and in house panel, which means the ground is 
> carrying current back to the generator in parallel with the neutral.
>
> I remember with some Honda portables we had to float the neutral at 
> the genset or the inverter would trip the generator's GFI when trying 
> to charge the batteries.
>
> On Fri, Dec 16, 2022 at 1:16 PM Dave Angelini Offgrid Solar via 
> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>     The easy answer is try another genset ! You have to be more
>     specific, did it ever work? Is it new? etc. Good Luck !
>
>     *Dave Angelini Offgrid Solar "we go where powerlines don't"
>     http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net
>     text 209 813 0060*
>
>
>     On 2022-12-16 10:04 am, Chris Daum via RE-wrenches wrote:
>
>>     Hi folks:
>>
>>     We have a new Magnum MS4024 mounted on an E-Panel using a MidNite
>>     Classic 150 and Whiz-Bang JR with power coming from an array of
>>     Trina TSM365-De06X-05(II) (three strings of three) with the
>>     ME-RC50 and a HUP SolarOne 6-85-14/24 battery.
>>     When we attempt to use the PFC (Power Factored Charger), the Gen
>>     Set’s GFCI outlets trip.  Thus far we have verified the
>>     connections are secure, assured that the gen set is grounded,
>>     disconnected the jumper within the E-Panel between the ground
>>     buss and neutral, checked AC voltages, removed the MNSPD’s from
>>     the buss(s)…  Stumped now on what an appropriate next step should
>>     be.  How do we get the PFC to function properly?  What are we
>>     missing?
>>
>>     Best,
>>
>>     Chris Daum
>>     Oasis Montana Inc.
>>     406-777-4309 or 4321
>>     406-777-4309 fax
>>     www.oasismontana.com <http://www.oasismontana.com>
>>
>>
>>
>>
>>
>>
>>
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     Pay optional member dues here: http://re-wrenches.org
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     There are two list archives for searching. When one doesn't work,
>>     try the other:
>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>     List rules & etiquette:
>>     http://www.re-wrenches.org/etiquette.htm
>>
>>     Check out or update participant bios:
>>     http://www.members.re-wrenches.org
>>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     Pay optional member dues here: http://re-wrenches.org
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     There are two list archives for searching. When one doesn't work,
>     try the other:
>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     http://www.re-wrenches.org/etiquette.htm
>
>     Check out or update participant bios:
>     http://www.members.re-wrenches.org
>
>
>
> -- 
>
> *Kirk Herander / **kirkh at vermont.solar*
>
> *Owner|Principal, VT Solar, LLC*
>
> */Celebrating our 31^st  Anniversary 1991-2022!!/*
>
> *www.vermont.solar* 
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20221216/1343d3f6/attachment.htm>


More information about the RE-Wrenches mailing list