Thanks everyone, the person I started with a SolArk asked me to call
them, so I've left a message. I'll let everyone know what the
determination is. Bradley raises a good point about shutting down the
back up loads panel. We would like to have an outdoor accessible
disconnect switch between the back up loads panel and the inverter so
that can happen more easily for first responders. I have to go back and
understand a few more things and will let you know. Thanks again. Chris
On 11/16/2022 10:14 PM, Bradley Bassett wrote:
> The issue as I see it is that the Tigo RSS Transmitter and the APsmart
> transmitter are both rated to draw up to 800ma. The 12VDC output of
> the Sol-Ark inverters is limited to 100ma. Since some have used this
> successfully I suppose that means that either these transmitters don't
> really use more than 100ma, or the 12VDC output of the Sol-Ark can
> actually handle more than that, or some combination of both. If I
> owned a Sol-Ark I'd test this to see what the answer is, but alas I do
> not. I design systems using a 48VDC to 12VDC power supply (Online
> Components has a Mean-Well device for a reasonable price, sorry no
> link from here) and a fairly rare IMO shutdown button (we have that)
> that has both NO and NC contacts. This is needed because to shut down
> the Sol-Ark inverter requires a NO contact that closes on initiation
> which is quite rare in RSD initiators. And you do still need to shut
> down the inverter as well as the RSD devices so that it does not
> continue to feed voltage back into the PV circuits (I think). This
> also shuts down the AC output of the Sol-Ark which tends to make the
> inspector happy. Since it also shuts down the inverter, that limits
> the battery to its own circuits, does this count as a battery
> disconnect also?? I'm seeing some inspectors calling out for battery
> disconnects which is much more problematic.
>
> Brad Bassett
> AEE Solar
>
> On Wed, Nov 16, 2022 at 4:27 PM Jerry Shafer via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Wrenches, Christopher
> I have done quite a few and per solark have always connected in
> the inverter with no issues, Now with that connecting to the
> output side it would do much the same work until it did not then
> shut off the modules.
> Fun times
>
> On Wed, Nov 16, 2022 at 6:33 AM Christopher Warfel via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi, We are doing our first system with these two devices. The
> inverter is SolArk 12P (mutimode) and the Tigo product for RS
> is the TS4F. Tigo has me a little bit walking in circles.
>
> I told them that SolArk says not to use the 12VDC RS output
> terminals for connecting the transmitter. I gave them the
> attached drawing which they ask for, which shows the
> transmitter connected to a 120VAC/12VDC breaker which they
> supply. They told me to wire the 120VAC source to the main
> service panel so the array would shut down on loss of power. I
> told them that is exactly NOTwhat I wanted to happen as that
> would stop the battery charging when there is a loss of
> utility power. I said I wanted the 120VAC source to be the
> back up loads panel. After about a week of calls and emails, I
> got an email back saying to use the SolArk 12VDC terminals for
> RS. I just emailed them a screen shot of the SolArk manual
> that says not to do that.
>
> At this point, I am asking anyone on the list to let me know
> how they wired the transmitter successfully. Thank you for any
> guidance, Chris Warfel
>
>
>
>
>
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't
> work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20221118/e40a8dad/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20221118/e40a8dad/attachment.jpg>
More information about the RE-Wrenches
mailing list