[RE-wrenches] Current Transformers (CTs) paralleled for multiple panel measure?
Jason Szumlanski
jason at floridasolardesigngroup.com
Thu Aug 11 14:50:53 EDT 2022
It will work from a technical standpoint, but you have to check if the
inverter can handle the current. Of course the current coming out of the
CTS will be a fraction of the actual current but there is going to be a
limit.
We do it on Enphase systems all the time for consumption monitoring.
Jason
On Thu, Aug 11, 2022, 2:26 PM Scot Arey via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Good day,
>
>
>
> We have a 400-amp meter can with no external disconnect; through the back
> of the meter can, the conductors go through wall to two inside 200-amp
> panels.
>
>
>
> We installed a Sol-Ark 15 (love it!) and had the included 320-amp CTs in
> the meter box but the utility has had change of heart and said nothing
> could go in there.
>
>
>
> A you know, the Solar-Ark can accept a pair of CTs to perform its “Limit
> to Home” functionality, but it can’t accept two.
>
>
>
> We’re considering paralleling the two separate pairs of CTs from each
> panel though an appropriate CT-wire sized connector to parallel the two L1
> CTs and the two L2 CTs into single wire outputs that can land in the inputs
> of the Solar-Ark. There is little possibility of extending the wires of the
> existing meter can to a new disconnect before it goes inside.
>
> Thoughts?
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220811/d126d529/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220811/d126d529/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220811/d126d529/attachment-0001.png>
More information about the RE-Wrenches
mailing list