[RE-wrenches] Enphase IQ7 versus IQ8

Jason Szumlanski jason at floridasolardesigngroup.com
Tue Jul 12 19:16:28 EDT 2022


Thanks, Nick. That is definitely an advantage that I didn't consider I
suppose. You're talking about the AC rating limit (microinverter combined
output). I think it would be rare around here because small battery systems
are not appropriate for central air conditioning backup. Most of the
systems we install are 40kWh, and that's cutting it very close for most
homes.

If my math is right, that allows about 23kW of PV (AC) with the IQ7 series
before you exceed the limit. We did one maxed out system with 66 x 415W
panels with IQ7A. We would be hard pressed to find a scenario where more PV
is necessary while 40kWh of battery capacity is sufficient.

While on the subject, it is important to note that only 80A of PV OCPD can
land on the smart controller busbar. In the application above, that meant
44 microinverters. The other 22 had to be feeder tapped on the load side of
the smart controller. That is not exactly an elegant solution. Totally
irrelevant to this conversation, but interesting to note.

I'm finding a lot of competitors in my market offering the IQ8 series
without sunlight backup and I have been scratching my head as to why. I
have been explaining to clients that it is not necessary to incur the extra
expense, but that is a hard sell when someone else is telling them they are
getting the latest and greatest. I don't want to roll over and join them,
but I also don't want to miss an important benefit that I haven't
considered.

Jason


On Tue, Jul 12, 2022, 7:03 PM Nick Soleil via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> That is correct, Jay.  You only need the rapid shutdown switch if you have
> IQ 8s and an IQ System Controller.
>
> One of the big advantages of the IQ 8 over IQ 7 when paired with storage
> is that the 1.5 PV to storage ratio does not apply, so you can install
> larger PV systems with smaller battery systems.
>
> Cordially,
>
> Nick Soleil
>
> Enphase Energy Senior Product Manager
>
> (707) 763-4784 x7267  // office
>
> (707) 321-2937  // cell
>
> *Powering What’s Next*™* | *The Enphase Energy Management System
> <https://enphase.com/en-us/products-and-services/envoy>
>
> NABCEP Certified Solar PV Installer #03262011-300
>
> California C10 Licensed Electrician #986315
>
> ------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf
> of Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent:* Tuesday, July 12, 2022 3:54 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jay <jay.peltz at gmail.com>
> *Subject:* Re: [RE-wrenches] Enphase IQ7 versus IQ8
>
> *EXTERNAL EMAIL* - *Use caution when responding, clicking, and/or
> downloading attachments.*
>
>
>
>
> Hi Jason
>
> And if you don’t have the smart controller/battery system then you do not
> need this proprietary rapid shut down switch correct?
>
> Jay
>
>
>
> On Jul 12, 2022, at 3:25 PM, Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> 
> Yes, they require a proprietary rapid shutdown switch that connects to the
> smart controller. This would be in addition to a visible load break
> disconnect if the utility requires it. You cannot fulfill both requirements
> with one switch, and it requires a line voltage circuit be run from the
> smart controller to the rapid shutdown switch.
>
>
>
> On Tue, Jul 12, 2022, 5:15 PM Mark Frye via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Do you need the additional switch if you use the Enphase battery?
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski via RE-wrenches
> *Sent:* Tuesday, July 12, 2022 11:38 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jason Szumlanski <jason at floridasolardesigngroup.com>
> *Subject:* [RE-wrenches] Enphase IQ7 versus IQ8
>
>
>
> I am trying to figure out why it is a good idea we use the IQ8 in anything
> other than a solar only backup scenario. If there are Enphase batteries
> involved, wouldn't the IQ7 do the same job on the roof? In a straight grid
> tied scenario, again the IQ7 would do the exact same thing. You would not
> have an upgrade path to solar only backup, of course.
>
>
>
> I'm just having a hard time understanding the value proposition of the IQ8
> in most of the situations I encounter. They cost significantly more, and
> you need an additional rapid shutdown switch when using batteries that can
> be quite a pain in some scenarios.
>
>
>
> Am I missing something about the switching speed, energy harvest
> capability, or the way they interact with batteries that makes them better?
>
>
>
> P.S. I am aware of the very small power output differences by model number
> and I am referring exclusively to 240 volt applications. I understand the
> 208 volt advantages of the IQ8.
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <https://urldefense.com/v3/__http://re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJe0CfSyQ$>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYISvg0nOQ$>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJj_4eGKg$>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYIMpOrPjw$>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYICPduJGQ$>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYKHzGjYsQ$>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <https://urldefense.com/v3/__http://re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJe0CfSyQ$>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYISvg0nOQ$>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYJj_4eGKg$>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYIMpOrPjw$>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYICPduJGQ$>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!J0D89H32QIeNiQ!0V6Viupc-8VYORVECQATdMKaJOpXjH6JOmgnqjF5RjB9RVhhygBgq0JWVaLGtsftGOsVhvP3evFLa1AbslfUJT9ZrYKHzGjYsQ$>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220712/28d97583/attachment.htm>


More information about the RE-Wrenches mailing list