[RE-wrenches] Enphase IQ7 versus IQ8
Jason Szumlanski
jason at floridasolardesigngroup.com
Tue Jul 12 17:24:45 EDT 2022
Yes, they require a proprietary rapid shutdown switch that connects to the
smart controller. This would be in addition to a visible load break
disconnect if the utility requires it. You cannot fulfill both requirements
with one switch, and it requires a line voltage circuit be run from the
smart controller to the rapid shutdown switch.
On Tue, Jul 12, 2022, 5:15 PM Mark Frye via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Do you need the additional switch if you use the Enphase battery?
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski via RE-wrenches
> *Sent:* Tuesday, July 12, 2022 11:38 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Cc:* Jason Szumlanski <jason at floridasolardesigngroup.com>
> *Subject:* [RE-wrenches] Enphase IQ7 versus IQ8
>
>
>
> I am trying to figure out why it is a good idea we use the IQ8 in anything
> other than a solar only backup scenario. If there are Enphase batteries
> involved, wouldn't the IQ7 do the same job on the roof? In a straight grid
> tied scenario, again the IQ7 would do the exact same thing. You would not
> have an upgrade path to solar only backup, of course.
>
>
>
> I'm just having a hard time understanding the value proposition of the IQ8
> in most of the situations I encounter. They cost significantly more, and
> you need an additional rapid shutdown switch when using batteries that can
> be quite a pain in some scenarios.
>
>
>
> Am I missing something about the switching speed, energy harvest
> capability, or the way they interact with batteries that makes them better?
>
>
>
> P.S. I am aware of the very small power output differences by model number
> and I am referring exclusively to 240 volt applications. I understand the
> 208 volt advantages of the IQ8.
>
>
>
> Jason Szumlanski
>
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220712/d543cd16/attachment.htm>
More information about the RE-Wrenches
mailing list