[RE-wrenches] Flex Power ONE FXR expansion
Sindelar Solar
Allan at sindelarsolar.com
Tue Jun 14 19:59:35 EDT 2022
Yes, but keep in mind that the X-240 autotransformer is only needed with
the FX/VFX inverters, and shouldn't be used with the FX-R/VFX-R series.
I learned this recently on a job where I replaced two older 24V VFX
units with new 48V VFX-R units and had to remove the balancing X-240.
Allan
On 6/14/2022 5:16 PM, Jerry Shafer via RE-wrenches wrote:
> Jeremy
> I have and used a second PS1 and added a transformer to connect the
> two, worked fine was just parts that all needed to connected
> Jerry
>
> On Tue, Jun 14, 2022, 4:08 PM Jeremy Rodriguez via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hello
> Does anyone have a solution for adding a second inverter to an
> single flex power pre wired panel, to achieve 120/240V ?
> I know it wouldn’t be on the same panel, but looking for an option
> here.
> Regards,
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado 81240
> _______________________________________________
>
--
*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*