[RE-wrenches] Plumbing/Mechanical Code for obstructions above plumbing vents
Rebekah Hren
rebekah.hren at gmail.com
Fri May 13 14:12:46 EDT 2022
Note that CA adopts UPC not IPC and the last time I checked there was no
exception to allow shorter vents under solar panels in the UPC, so it
differed from IPC allowance.
If this has changed, would be glad to be know about it!
Cheers,
Rebekah
On Fri, May 13, 2022, 10:51 AM Brian Mehalic via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> The 2021 IPC (Section 903) requires vents to terminate at the height
> specified by the AHJ (in fact the text of the document literally says "not
> less than [NUMBER] inches (mm) above the roof" which I believe in general
> is based on 6 inches above anticipated snow cover.
>
>
> The 2021 IPC also specifically addresses things like PV modules over vents
> - when the vent is covered, like by a PV module, and thus cannot be
> covered by snow, the vent can terminate 2 inches above a sloped roof. There
> must be an "open area for the pipe to the outdoors" not less than the I.D.
> of the pipe, and there must be means to prevent birds/rodents from
> entering/blocking the pipe.
>
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional⢠R031508-59
> National Electrical CodeĀ® CMP-4 Member
> (520) 204-6639
>
> Solar Energy International
> http://www.solarenergy.org
>
> SEI Professional Services
> http://www.seisolarpros.com
>
>
>
> On Fri, May 13, 2022 at 9:53 AM Bruce Leininger via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hello. I'm wondering if there is a code reference for the allowable
>> clearance above a plumbing vent. I've run into several jurisdictions that
>> ask for the clearance to be at least 2x the diameter of the vent pipe. I'm
>> wondering if there are any code references to back this up or any code that
>> specifically prohibits obstructions (like solar panels) above plumbing
>> vents.
>>
>> Thanks all!
>>
>> Bruce
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220513/855ad0c3/attachment.htm>
More information about the RE-Wrenches
mailing list