[RE-wrenches] AC Coupled Tesla system

Marco Mangelsdorf marco at pvthawaii.com
Thu Apr 28 21:02:34 EDT 2022


Max rating of the Gateway2 is 200A.

Regarding a generator input, you're correct, there's no means that I'm
aware of to integrate a backup generator with the Tesla equipment that
would interact with the solar and storage.
marco

On Thu, Apr 28, 2022 at 5:45 PM William Miller via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Friends:
>
>
>
> I have two questions about AC coupling Tesla systems:
>
>
>
> 1.   Are there limits on how much power can be AC coupled through a Tesla
> gateway?  Does it depend on the quantity of power-walls connected?
>
> 2.   I understand a Tesla system does not have a separate generator input
> so if a generator is to be incorporated, a transfer switch is required
> upstream of the sole AC input.  If the generator were to start on a sunny
> day, would the gateway protect the generator from receiving sell amps from
> the AC coupled inverters?
>
>
>
> Thanks in advance for any information that you are allowed to share.
>
>
>
> Sincerely,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220428/8152cbfc/attachment.htm>


More information about the RE-Wrenches mailing list