The Schneider RSD switch has a Tigo transmitter, which is no longer SunSpec
compliant. SunSpec devices do NOT work. I know for certain that the APsmart
devices do not work.
Fire Raptors are very robust and might be a good choice for off grid where
reliability is paramount. But they come with 6ft cables for both control
and string wires so you have to figure out what to do with all that nest of
wire under the array. And you have to have a 24VC power source up to the
roof to power them. The manual shows one FireRaptor for two modules, but
unless you have very low voltage modules that is not going to meet code.
One for each module is required to stay under the 80 VDC limit.
Brad
On Tue, Apr 19, 2022 at 3:06 PM Jerry Shafer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> You may want to look at fire raptor as a RSD option.
> Jerry
>
> On Tue, Apr 19, 2022, 9:42 AM jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> HI All
>>
>> I’ve got a project coming up that has specified a Schneider XW 80/600
>> controller.
>>
>> Its going to need RS.
>>
>> Is the only product still the Tigo TS4-A-F?
>>
>> thanks
>>
>> jay
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220419/9fb6a3f4/attachment.htm>
More information about the RE-Wrenches
mailing list