[RE-wrenches] Sol-Ark 15k

Darryl Thayer darylsolar1 at gmail.com
Sun Apr 17 11:28:59 EDT 2022


The tap rule says you can reduce to 10% of the nominal size for 10 feet and
protect at the downstream OCPD or 25% for 25 feet for solar with multiple
sources see 705

On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> That's what I'm thinking. You would need to use a 200A conductor to a
> separate load out OCPD before downsizing the wire. I guess there are pros
> and cons, but it seems this is geared toward whole house backup for 200A
> services. I'm eager to get an opportunity to use it in that scenario.
>
> Jason
>
>
>
>
> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Jason,
>>
>> Any additional OCPD downstream of the 200A load output breaker could
>> allow for a smaller wire size to be used at these terminals. For example,
>> load output conductors run to a 100A main breaker panel board.  Obviously
>> depending on circumstances, a #4 copper could fit the bill.
>>
>> What I’m not extremely  excited about with the new design is that in an
>> off-grid scenario with a generator and smart load, we would now need to
>> integrate an AC disconnect for generator input (grid)  and either a fused
>> disconnect or loads panel for any smart load output. With the 12K unit, the
>> integrated breakers help cut down on BOS and install time.
>>
>> -Chris
>>
>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hello, The overcurrent device is to protect the conductors.  you can put
>>> any size wire, but you must protect with the overcurrent device.  REmember
>>> in solar equipment; you may have more than one supply source.  The DC best
>>> example is solar modules connected in parallel,      on
>>>
>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> You must meet all expected source output potentials within the design
>>>> and operating limits, as long as the distribution panel and connected
>>>> wiring is rated for the max output of the protected source then you are
>>>> good. A 200 ATS connected to a 10 kW genny does not require 2/0 as it will
>>>> never meet that rating. Just remember its whatever the max output can be
>>>> plus your margin.
>>>>
>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> Hi Jason,
>>>>>
>>>>> You bring up a valid point….in an off-grid scenario with the 15k do
>>>>> you size the conductors to the continuous capacity, surge capacity or the
>>>>> OCPD of the unit?
>>>>>
>>>>> -Chris
>>>>>
>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>>>>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>>>> jason at floridasolardesigngroup.com> wrote:
>>>>>>
>>>>>>> I'm not following the wiring diagrams for this new inverter. It has
>>>>>>> 200A pass-through capability with an integrated 200A load disconnect. But
>>>>>>> then it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>>>>>
>>>>>>> In an off-grid scenario where there is no generator, the max
>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection could be
>>>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>>>> implemented if the 200A breaker is integrated? Do you have to run a short
>>>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4?
>>>>>>>
>>>>>>> Jason Szumlanski
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>
>>>>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220417/2ad9c29b/attachment.htm>


More information about the RE-Wrenches mailing list