[RE-wrenches] Sol-Ark 15k
Chris Sparadeo
sparadeo.chris at gmail.com
Sat Apr 16 22:06:32 EDT 2022
Jason,
Any additional OCPD downstream of the 200A load output breaker could allow
for a smaller wire size to be used at these terminals. For example, load
output conductors run to a 100A main breaker panel board. Obviously
depending on circumstances, a #4 copper could fit the bill.
What I’m not extremely excited about with the new design is that in an
off-grid scenario with a generator and smart load, we would now need to
integrate an AC disconnect for generator input (grid) and either a fused
disconnect or loads panel for any smart load output. With the 12K unit, the
integrated breakers help cut down on BOS and install time.
-Chris
On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hello, The overcurrent device is to protect the conductors. you can put
> any size wire, but you must protect with the overcurrent device. REmember
> in solar equipment; you may have more than one supply source. The DC best
> example is solar modules connected in parallel, on
>
> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> You must meet all expected source output potentials within the design and
>> operating limits, as long as the distribution panel and connected wiring is
>> rated for the max output of the protected source then you are good. A 200
>> ATS connected to a 10 kW genny does not require 2/0 as it will never meet
>> that rating. Just remember its whatever the max output can be plus your
>> margin.
>>
>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hi Jason,
>>>
>>> You bring up a valid point….in an off-grid scenario with the 15k do you
>>> size the conductors to the continuous capacity, surge capacity or the OCPD
>>> of the unit?
>>>
>>> -Chris
>>>
>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>> jason at floridasolardesigngroup.com> wrote:
>>>>
>>>>> I'm not following the wiring diagrams for this new inverter. It has
>>>>> 200A pass-through capability with an integrated 200A load disconnect. But
>>>>> then it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>>>
>>>>> In an off-grid scenario where there is no generator, the max
>>>>> continuous output is 62.5A, so I assume 80A circuit protection could be
>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>> implemented if the 200A breaker is integrated? Do you have to run a short
>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4?
>>>>>
>>>>> Jason Szumlanski
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> --
>>> Chris Sparadeo
>>>
>>>
>>> C_802-369-4458
>>> H_802-728-3059
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220416/81ad0c05/attachment.htm>
More information about the RE-Wrenches
mailing list