[RE-wrenches] Sol-Ark install
Maverick Brown
maverick at mavericksolar.com
Wed Apr 13 21:54:12 EDT 2022
Ron
The Sol-Ark has two MPPT channels and has two separate landing spots for each MPPT channels. Each landing pair needs matching strings. 8 AWG wire barely fits so the Sol-Ark PV terminals so they may only be rated for 10AWG.
I’m assuming you have a ground array The most common stringing method would be to use a trench with conduit and THHN wire. You could also sleeve a direct-burial cable into the ground. Calculate the voltage drop over the distance to make sure 10AWG is adequate. If not, then make a junction, like a MidNite or Outback combiner or an IMO switch at the array to get up the right wire size, with an added MidNite Surge Protector or EMP shield device. If it’s a long distance (larger wire size), add another combiner at the inverter building entrance to get back to 10 AWG.
https://practicalpreppers.com/product/imo-4-pole-16-amp-dc-disconnect/
Also, The Sol-Ark sizing guide helps with string calculations.
https://www.sol-ark.com/solar-panel-sizing/SolarPanelSizing.html
Contact me off list with additional questions.
Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
• Solar Commander Remote Power
• SunFlow Systems Cathodic Protection
maverick at mavericksolar.com
512-460-9825
> On Apr 12, 2022, at 9:42 PM, Ron Young via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install. Because the max DC voltage is 500v at 18a and the PV I’m using is 40v DC each I will have to create three strings each 480v. What would be the best choice for a home run wire? I’ve always used smaller strings with micro inverters, a combiner at the array and a single Teck home run cable but the string inverter presents a different scenario and it looks like I’ll need to use three home run cables, one for each string.
>
> Ron Young
>
> earthRight Products - Solareagle.com
> Alternative Energy Solutions ~ Renewable Energy Products
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220413/f3224ff4/attachment.htm>
More information about the RE-Wrenches
mailing list