[RE-wrenches] Sol-Ark grid tie question
Jeff Clearwater
jeffc at villagepowerdesign.com
Fri Apr 1 15:27:01 EDT 2022
Hey Jason,
So yes the Load will be hot with Grid Pass-thru - The Sol-Ark has 3
breakers - Grid (63A) - GEN (50A) - Load (63A) (European type
breakers). I have not experienced the delay that Nick observed but
perhaps cause I've always had batteries on them.
The nice thing is that with the software and phone app on both you will
be able to program all settings remotely for the client.
As to the Anderson battery disconnect idea - my biggest issue with all
battery systems these days is folks not using proper OCP on Parallel
batteries. With 48 Volt Lithium now in small increments if you parallel
6 server rack type 100 A rated batteries together you are already at 600
amps and then if you parallel 4 racks of 6 you are at 2400 Amps! Yes
each battery has a 100 A Breaker but I see few installers really dealing
with the fault possibilities in between.
Attached is a Victron Fuse setup I did for 30 100 AH batteries on 4
Sunny Islands. It was 5 racks of 6 batteries. I put each of the 5
racks on a 200 Amp Fuse and each Sunny Island on a 200 A fuse in this box.
So with the Anderson's you might want to think what amperage fault
potential is where when you unplug.
Hope that helps!
Best,
Jeff
> Jason Szumlanski via RE-wrenches
> <mailto:re-wrenches at lists.re-wrenches.org>
> April 1, 2022 at 11:52 AM
> Fantastic. Thanks!
>
> As a follow up, he's considering connecting a battery bank with an
> Anderson connector. This is not the golf cart scenario I mentioned in
> another thread, but he wants to be able to wheel away his battery into
> storage. Don't ask me why... I can't figure it out myself. Do you see
> any issues with this? I guess the question I have is what happens when
> the battery is connected and he's on grid and he decides to disconnect
> the battery? I'm guessing nothing, but I could be wrong. Will he need
> to change the settings back to grid-tie only?
>
> Jason
>
>
>
>
>
> *
>
> *
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> Nick A Lucchese via RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
> April 1, 2022 at 11:29 AM
> Jason, this will work just fine. I’ve not fully embraced a transition
> to their products for my clients yet but had one recently where the
> customer insisted on this for their project and I was in the exact
> scenario while we waited for the battery to arrive. No external bypass
> required for this reason. However it does not work without a minor
> setting activation and even then there was a 10-20 second delay before
> the relay is closed and the utility will pass through.
>
> Nick
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> Jason Szumlanski via RE-wrenches
> <mailto:re-wrenches at lists.re-wrenches.org>
> April 1, 2022 at 9:29 AM
> If you set up the inverter in a straight grid tie mode, does it still
> pass power through to the load terminals when on grid?
>
> I ask this, because a client wants us to connect it with a backup load
> panel but no battery right now. He wants to add the battery later.
>
> My other thought is to install a bypass switch to pass grid power
> directly to the subpanel, which would act as a service bypass for the
> future anyway.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220401/4308abee/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IMG_8426.jpeg
Type: image/jpeg
Size: 275401 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220401/4308abee/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IMG_8425.jpeg
Type: image/jpeg
Size: 277348 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220401/4308abee/attachment-0001.jpeg>
More information about the RE-Wrenches
mailing list