[RE-wrenches] Sol-Ark grid tie question
Nick A Lucchese
lucchesesolar at me.com
Fri Apr 1 14:29:02 EDT 2022
Jason, this will work just fine. I’ve not fully embraced a transition to their products for my clients yet but had one recently where the customer insisted on this for their project and I was in the exact scenario while we waited for the battery to arrive. No external bypass required for this reason. However it does not work without a minor setting activation and even then there was a 10-20 second delay before the relay is closed and the utility will pass through.
Nick
> On Apr 1, 2022, at 9:29 AM, Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> If you set up the inverter in a straight grid tie mode, does it still pass power through to the load terminals when on grid?
>
> I ask this, because a client wants us to connect it with a backup load panel but no battery right now. He wants to add the battery later.
>
> My other thought is to install a bypass switch to pass grid power directly to the subpanel, which would act as a service bypass for the future anyway.
>
> Jason Szumlanski
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list