[RE-wrenches] Equipment for 400 Amp Service Supply Side & 200A PV
Jeff Clearwater
jeffc at villagepowerdesign.com
Tue Mar 29 14:35:39 EDT 2022
Thanks Vincent- thanks I’ve used this panel in the past but do you you know if “Manual Bypass” is the same as test link bypass - suitable for PGE/Western Utilities?
Sent from my iPhone
> On Mar 29, 2022, at 10:38 AM, Vincent Jolissaint via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Hi Jeff,
>
> I prefer this panel for this need. it has a dedicated left side for (2) @100A breakers max or (1) @ 200A max PV backfeed.
>
> https://assets.new.siemens.com/siemens/assets/api/uuid:4e2c50f4-f20a-481c-8cb4-bd817cd7cb04/sie-fl-400srmetercombo.pdf
>
> In addition, it has all the features of a typical 2x200A service panel.
>
>
> With Regard,
> Vince Jolissaint
> Cobalt Power Systems Inc. | Director of CAD Services
> 2557 Wyandotte St. | Mountain View CA 94043
> Office: 650.938.9574 | E-Mail Vincentj at cobaltpower.com
>
>>
>> From: Jeff Clearwater <jeffc at villagepowerdesign.com>
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> Subject: [RE-wrenches] Equipment for 400 Amp Service Supply Side & 2
>> 200s
>> Message-ID:
>> <84bbb4d9-73ca-f7a3-2d2c-952b3541326b at villagepowerdesign.com>
>> Content-Type: text/plain; charset="utf-8"; Format="flowed"
>>
>> Good Day Wrenches,
>>
>> Does anyone know of a 400 Amp Meter/Main that can accomplish the following?
>>
>> 1)? Provide 2 x 200 Main Breakers for Loads
>> 2) Provide an easy supply side tap point for 160 Amps of Grid-tie Solar
>> (so basically a 200 Amp backfeed)
>>
>> I'm considering using an Eaton 324 N
>> <https://www.rexelusa.com/p/525405/eaton-b-line/400a-4p-4-jaw-meter-socket/782051622102/324-n>?
>> (Eaton B-Line 324 N 400A, 320 A cont. 4P, 4 Jaw, Meter Socket W Link
>> Bypass Facilities) but I'm not sure I can double lug it and then also
>> tap off of one of the 200 Amp lines with another tap (using Ilsco
>> IPC-250-4/0
>> <https://www.ilsco.com/Ilsco/ccrz__ProductDetails?sku=IPC-250-4%2F0-ILSM-ILS&cclcl=en_US>
>> splice connectors).
>>
>> Thanks!
>>
>> Jeff
>>
>>
>> ~~~~~~~~~~~
>> Jeff Clearwater
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>>
>>
>> linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
>> www.villagelab.net <http://www.villagelab.net>
>> www.villagepowerdesign.com <http://www.villagepowerdesign.com>
>> cell - 413-559-9763**
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220329/01c487b5/attachment.htm>
More information about the RE-Wrenches
mailing list