[RE-wrenches] Flickering lights on off grid AC coupled radian system
Chris Sparadeo
sparadeo.chris at gmail.com
Wed Feb 2 15:08:37 EST 2022
Hi Lars,
It sounds like an issue with frequency shifting. I’m guessing that this is
mostly happening when the battery is full. The Radian is shifting its
frequency (to probably around 63-64 Hz) to turn of the AC coupled PV
inverter. Some lights and electronics don’t like this and can either
flicker, or turn off. This is one of the issues with AC coupling that makes
it a less than ideal fit for off-grid application.
One option would be to look into replacing the lights with something that
has a larger tolerante for change in frequency. Another option might be to
lower the inverter’s grid frequency tolerance so that it trips and turns
off before the flights end up freaking out.
Hope this helps.
-Chris
On Wed, Feb 2, 2022 at 2:59 PM Lars Ortegren <lars at cal-solar.com> wrote:
> Wrenches,
> I'm hoping to solve an issue we've had with a couple of our off grid AC
> coupled systems. We have had multiple reports of different LED and
> traditional ballasted fluorescent systems "flickering" during the day when
> the AC systems are producing power. We havent had issues with other off
> grid AC coupling using Sunny Islands, or even old VFX inverters, but this
> does seem to be an issue directly related to the Radians.I'm wondering if
> any of you have had experience with this, and if you found any hacks to
> "clean up" the power?
>
> --
> Lars Örtegren
> General Manager
> Co-Founder
> Worker-Owner
> He/Him <https://www.mypronouns.org/>
> <https://www.cal-solar.coop/>
> 530 274 3671 | ext 307 <530+274+3671>
> lars at cal-solar.com
> www.Cal-Solar.coop <https://www.cal-solar.coop/>
> 149 E. Main St, Grass Valley, CA 95945
> <https://www.google.com/maps/search/149+E.+Main+St,+Grass+Valley,+CA+95945?entry=gmail&source=g>
> NABCEP: #PVI-091110-89
> CSLB #779624 <https://www.cal-solar.coop/we-are-a-b-corp>
> <https://www.amicussolar.com/> <https://www.nabcep.org/>
>
> <https://californiasolarco.com/quote/>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220202/19d5efd6/attachment.htm>
More information about the RE-Wrenches
mailing list