[RE-wrenches] Rapid Shutdown for Off-grid systems

William Miller william at millersolar.com
Tue Feb 1 13:24:30 EST 2022


Ray:



Thanks for that input.  I was hoping I was wrong.  I looked for that
discussion in the archives but could not find it.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Ray
*Sent:* Tuesday, February 1, 2022 10:11 AM
*To:* re-wrenches at lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



 Ground mounts do NOT require RSS.  We hashed this out years ago on the
Wrenches list, when NEC 2017 came out.

See Figure 690.1(B) Note (2): *" The PV system disconnect in these diagrams
separates the PV system from all other systems".*

Thus, the PV disconnect is defined as the transition point from the PV
system to all other systems, like battery or inverter systems. The
installer/ designer decides where to put that disconnect.  I usually put it
on the wall before it goes into the building, and I have never had an
inspector question that.

Thanks,

Ray Walters

Remote Solar

303 505-8760

On 2/1/22 10:06 AM, William Miller wrote:

Jay:



Here is the text from 2017:



*690.12 Rapid Shutdown of PV Systems on Buildings. PV*

*system circuits installed on or in buildings shall include a rapid*

*shutdown function to reduce shock hazard for emergency*

*responders in accordance with 690.12(A) through (D).*



*Exception: Ground mounted PV system circuits that enter buildings, of*

*which the sole purpose is to house PV system equipment, shall not be*

*required to comply with 690.12.*



The wording is interesting.  The requirement is directed at “PV system
circuits…”, not PV arrays.  The passage does not specify where the PV
feeding those circuits is located, it just addresses where the circuits
are, specifically “in or on a building.”



The only circuits that are exempt are those feeding a building that serves
only one purpose, to house PV equipment.  For circuits that enter building
with other uses—homes, garages, barns, workshops, etc.-- it would seem
there is a requirement to have rapid shutdown systems (RSS).



Reading through the rest of the section, I don’t see any language that gets
us out of the requirement to reduce voltages to less than 80 volts within
30 seconds inside the array boundary, as in module level shutdown,
regardless of roof-top or ground-mount.  Although the 2020 code includes
some differing language, I don’t see it as exempting ground mount systems.



The moral of the story is this:  For ground-mounts:  either install RSS or
put your equipment (inverters, charge controllers, batteries, BOS) in a
separate building housing only that equipment.



I don’t necessarily like the requirement, but I think it exists.  Jay, or
anyone, please, please tell me I am reading this incorrectly.



By the way, regarding battery circuits, here is a quote from a post by Bill
Brooks on March 16, 2016:



*In the 2017 NEC, we were very careful to carve out all batteries and
loads,*

*that were previously part of PV systems, and place them in their own*

*articles.*



I have not read through the battery sections of the code to verify this, I
am taking Bill at his word.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* Jay [mailto:jay.peltz at gmail.com]
*Sent:* Tuesday, February 1, 2022 6:07 AM
*To:* william at millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



2017 code has a specific exception/clarification for ground mount solar
that it does not need RS.

It’s in the first line after 690.12



Jay



On Feb 1, 2022, at 12:13 AM, William Miller <william at millersolar.com> wrote:



Jerry:



Yes it is required.  Rapid Shutdown:  NEC 690.12.  All buildings except
dedicated solar buildings.  Read it and weep.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* Jerry Shafer [mailto:jerrysgarage01 at gmail.com]
*Sent:* Monday, January 31, 2022 7:21 PM
*To:* William Miller; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



William

Are you sure RSD is required on a non habitable building, historically its
not required. Now that being said we use fire raptor with the best results,
yes it takes an extra conduite and might require a button and power supply
depending on inverter application.

Jerry



On Mon, Jan 31, 2022, 9:57 AM William Miller <william at millersolar.com>
wrote:

Friends:



It is quite rare for us to install off-grid systems on roof-tops.  We have
one coming up with about 20kW on a large barn roof.  This will be our first
off-grid with a module-level rapid shutdown requirement.  I see no
exemptions from RSS for off-grid systems in the code.  I have looked at the
options and this is what I have found:



1.   Fire Raptor

2.   Tigo TS4-F

3.   AC coupling with micro-inverters or optimizers



No one of these approaches seems ideal.  The fire raptor requires extra
wiring for control leads.  The Tigo requires a wireless control system
which worries me about reliability.  With AC Coupling systems floating the
proposed AGM batteries may be awkward.  Furthermore, with AC coupled
systems one cannot charge batteries unless the mini-grid is operational, a
big problem.



Have any of you implemented module-level RSS on a battery-based inverter
system?  I looked in the archives and found no threads that apply.  Thank
in advance.



William Miller
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220201/e04ffcde/attachment.htm>


More information about the RE-Wrenches mailing list