I’m facing this same issue.  In the past we’ve used the old SQD disco’s near the inverter and fuses in combiners near the array, but they’re big and expensive.  

Anyone used these or see any issue with these:
https://www.industrialcontroldirect.com/dc-disconnect-si16-pel64r-4-p-4080.html?gclid=Cj0KCQiA_8OPBhDtARIsAKQu0gYOEY75OrhrQHsrDVHHCsUd-E6SiYwEcCi1FwY5vWua5iIFl7ovNxMaAroLEALw_wcB <https://www.industrialcontroldirect.com/dc-disconnect-si16-pel64r-4-p-4080.html?gclid=Cj0KCQiA_8OPBhDtARIsAKQu0gYOEY75OrhrQHsrDVHHCsUd-E6SiYwEcCi1FwY5vWua5iIFl7ovNxMaAroLEALw_wcB>

Or these:
https://www.industrialcontroldirect.com/dc-disconnects-316/panel-mount-dc-switch-421/?zenid=bo3nrdji7umkvsr93hslphj4g4 <https://www.industrialcontroldirect.com/dc-disconnects-316/panel-mount-dc-switch-421/?zenid=bo3nrdji7umkvsr93hslphj4g4>

Seems like a nice clean and not terribly expensive option.  Totally agree that Schneider should have provided us with a solution in the PDP.

Best Regards,
Jeremy Coxon NABCEP # 091308-21
MWBE Certified



On Jan 26, 2022, at 4:19 PM, re-wrenches-request at lists.re-wrenches.org wrote:

Send RE-wrenches mailing list submissions to
	re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>

To subscribe or unsubscribe via the World Wide Web, visit
	http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>
or, via email, send a message with subject or body 'help' to
	re-wrenches-request at lists.re-wrenches.org <mailto:re-wrenches-request at lists.re-wrenches.org>

You can reach the person managing the list at
	re-wrenches-owner at lists.re-wrenches.org <mailto:re-wrenches-owner at lists.re-wrenches.org>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of RE-wrenches digest..."
When responding to posts within the Digest, be sure to restore the Subject: line to the original, and please edit out any extraneous lines from the quoted message.
Today's Topics:

  1. Re: High Voltage Breakers for Conext Mppt-80-600 (Pieter Huebner)

From: "Pieter Huebner" <pieter at offgridenterprises.org <mailto:pieter at offgridenterprises.org>>
Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Date: January 26, 2022 at 4:19:48 PM EST
To: <william at millersolar.com <mailto:william at millersolar.com>>, "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>


I must caution those who are considering the use of touch safe fuse holders in distribution panels. If one of those fuse holders were to be opened under load you will very likely have a fire. Always be sure to only install touch safe fuse holders in such a manner that they cannot be opened by un trained personnel, Those fuse holders are not load break rated.
Pieter
 
<image001.png>
 
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of William Miller
Sent: Wednesday, January 26, 2022 12:05 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
 
Michael:
 
This seems like a rather stunning oversight—offering a charge controller without any means to integrate it into the BOS built by the same manufacturer.
 
Just now I laid a 600 VDC rated touch-safe fuse holder over a QOU breaker.  The fuse holder is smaller than the breaker so it would fit in the PDP.  The fuse holder would be a bit recessed which may look awkward and impede the opening of the fuse holder.  I do know you can buy DIN rail of varying height.  Maybe you could drill out the rivets on the DIN rail and replace a short section of it with high profile DIN Rail and make a somewhat elegant solution???
 
Good luck.
 
William Miller
 
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
 
 
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Michael Morningstar
Sent: Tuesday, January 25, 2022 4:53 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
 
Thanks guys,
Just wanted to make sure I wasn’t missing something. Curious that Schneider doesn’t have higher voltage input breakers.
 

On Jan 25, 2022, at 4:15 PM, Tump <tump at swnl.net <mailto:tump at swnl.net>> wrote:
 
I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that
On Jan 25, 2022, at 7:04 PM, Tom Duffy <Tom at solar-biz.com <mailto:Tom at solar-biz.com>> wrote:
 
Hi Mike
 
No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they’re DIN rail
 
Tom Duffy
Senior Solar Design Engineer
 
Supply chain crunches brought on by the pandemic and Omicron’s toll on the workforce are causing shortages of goods. Most analysts agree that rising prices — not just in the US, but also across the world — are largely consequences of the Covid-19 crisis rather than policy errors by governments or central banks.
Infectious waves have closed factories in Asian manufacturing hubs and caused chaos in transporting products to US markets, creating a spike in demand. Also Americans have cash to burn after two years of canceled vacations, closed restaurants and working from home, a major factor supercharging the price surge. 
<image001.png>
tom at solar-biz.com <mailto:tom at solar-biz.com>
MAIN TOLL FREE: 888-826-0939
DIRECT: 888-503-6772
International: 001-575-539-2111
PANAMA: 507-836-5588 X 122
FAX: 520-844-8442
www.thesolarbiz.com <http://www.thesolarbiz.com/>
CONFIDENTIALITY NOTICE:  This electronic mail message and any attached files contain information intended for the exclusive use of the individual or entity to whom it is addressed and may contain information that is proprietary, privileged, confidential and/or exempt from disclosure under applicable law.  THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL TRANSMISSION IS CONFIDENTIAL.  If you are not the intended recipient, you are hereby notified that any viewing, copying, disclosure or distribution of this information is strictly prohibited and may be subject to legal restriction or sanction.  Please notify the sender immediately by electronic mail of any unintended recipients and delete the original message without making any copies. 
 
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>> On Behalf Of Michael Morningstar
Sent: Tuesday, January 25, 2022 1:02 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>>
Subject: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
 
Wrenches,
 
Can anyone direct me to PV input breakers that are rated up to 600VDC that would work in a Conext Distribution Panel? From what I can tell, Schneider only offers breakers up to 160VDC.
 
Thanks,
Michael
 
 

 
          Michael Morningstar
 
          Morningstar Electric
          PO Box 1494
          Mount Shasta, California 96067
          530-921-0560
          CSLB 949635
 
  <image002.gif>
 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
 
Tump <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>3391 at gmail.com <mailto:3391 at gmail.com>       www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights       
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401                              
                              Blair "TUMP" May
               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer" 
   
              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"
 
 

 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
 
 

 
         Michael Morningstar
 
         Morningstar Electric
         PO Box 1494
         Mount Shasta, California 96067
         530-921-0560
         CSLB 949635
 
  <image003.gif>
 


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/e6ae9e6b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SWPS 16yr Logo copy.jpg
Type: image/jpeg
Size: 14371 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/e6ae9e6b/attachment.jpg>


More information about the RE-Wrenches mailing list