Hello Mac
Thank you for sending me the Optics site name I was able to find some info on the FM100 situation.
There was an arc fault at 01/20/22 6:34 AM
The FM worked until that point in time.
Arc fault can be difficult especially in remote situations. I believe the FM 100 arc fault works well.
I am not aware of any related issues.
The manuals states that both PV+ and PV- wires be routed through the Rogowski coil in opposite directions
This helps to reduce (hopefully eliminate) false readings. Unfortunately the fault has to be reset manually.
Below are some screen shot from Optics
[cid:image001.png at 01D8128C.E5B9A560]
18th 19th 20th
[cid:image002.png at 01D8128C.E5B9A560]
https://outbackpower.com/downloads/documents/charge_controllers/flexmax_100_afci/fm100_afci_manual.pdf
see page 21 on arc fault
page 57
[cid:image003.png at 01D8128C.E5B9A560]
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Mac Lewis
Sent: Tuesday, January 25, 2022 4:42 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Silent FM100
CAUTION: This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe.
Hello Wrenches,
I have a recently installed Outback system, (Radian, FM100, Mate 3s) that was humming along great for about a month but for some reason the FM 100 stopped charging. It went through a full charge day, but has stayed in Silent state ever since. No event was logged (via Optics at least) and we are well within its current and voltage bounds.
I can see ~ 210 V on the PV input via Optics
We are below rebulk and float thresholds.
I have tried to remotely trigger a bulk charge, an eq charge etc. I have tried remotely rebooting the Mate. Any other things I should try remotely? I am trying to avoid a long snowcat ride!
Thanks
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/08f3146d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 87834 bytes
Desc: image001.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/08f3146d/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 10801 bytes
Desc: image002.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/08f3146d/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 258873 bytes
Desc: image003.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/08f3146d/attachment-0002.png>
More information about the RE-Wrenches
mailing list