[RE-wrenches] Outback Charge controller breakers (was Mixing Outback FM100 CC with Fm80 or 60.)

William Miller william at millersolar.com
Tue Jan 25 16:30:32 EST 2022


Colleagues:



Lones, thanks for being in the hot-seat on this and many other Outback
related issues.  I need to remind myself that I do not know what engineers
and product managers have to go through to get products listed and comply
with all of the attendant regulations.  So when some application does not
make sense, it may be because of bureaucracy I am not familiar with.



Also, if sometimes it seems like I am whining or nit-picking, please
remember I consider Outback to be the best off-grid equipment on the
market.  I strive for excellence in my work and sometimes to get that I
have to ask lots of questions.



Let me stipulate that I am not going to start installing 300 volt rated
inverter breakers on systems with FM100 charge controllers.  I don’t think
any other wrench is going to do that and it does not seem Lones is
suggesting that.  I am willing to install an FM100 in the same system with
and FM60 or FM80.  I will use external GFDI protection.



However, in reviewing the Outback installation manuals, it is not clear how
the GFDI breakers are installed and sized.  Different manuals show
different wiring diagrams and different breaker sizing specifications.
Here is a breakdown of what I found and what I decided for my own projects:



GFDI breaker placement:



Various Outback manuals for the  GFDI breakers and charge controllers show
the GFDI being placed either before or after the charge controller.  I
checked the NEC and the requirement is this: either the current carrying
conductors of the faulted circuit be disconnected or the inverter or charge
controller cease supplying power.  It is important to remember these GFDI
circuits do not resolve a ground fault, they just let the system user know
(somewhat vaguely, I might add) that something is wrong.  The user only
knows, eventually, that PV charging has stopped.  I believe either NEC
requirement is met with the GFDI either before or after the charge
controller, so I will suit myself on a case-by-case basis.  Combiner
breakers will act as manual PV disconnecting means.



Multiple GFDI breakers:



What if you need more than 4 charge controllers, or you need GFDI breakers
of different values?  Either scenario requires more than one GFDI breaker
assembly.  If you install more than one GFDI and wire them each as
indicated-- with one side of each 0.5 amp sense pole to the negative and
the other to ground, you are paralleling the sense poles.  Theoretically,
this allows double the fault current (for two GFDI breakers, triple for
three, etc.).  Is this OK?  This wiring does mean if one GFDI trips, all
trip.  You could wire the sense breakers in series and maintain the 0.5 amp
trip level, but likely only one GFDI will trip in a fault.  I have not
decided which method I would recommend.  Anyone have an opinion?



Breaker sizing:



Outback manuals give conflicting advice on breaker sizing.  In the old days
I had applied the 125% rule to the CC nameplate and put this sized breaker
before and after the charge controller.  After some thought, I conclude
this is not correct.  There are different criteria for input and output
breaker sizing, as indicated:



Input breakers:  Proper design would have you calculate 125% the Isc of the
connected PV array and pick a breaker the next standard size up from that
value.  That breaker must have a voltage rating greater than the highest
Voc at the coldest possible temperature.



Output breakers:  CC output breakers will never be subjected to Isc
currents.  If there is a short circuit in the output side of a charge
controller, the large ampacity of the battery bank will open the output
breaker.  I suggest that the proper sizing method is to use the nameplate
wattage of the attached PV array and divide that by the lowest expected
battery voltage.  This gives the highest possible Imp.  Multiply that by
125% and pick the next larger breaker.  That breaker must be voltage rated
greater than the highest battery voltage expected.



Documents missing from the Outback web site:  I looked all over and I
cannot find these documents:



A current version of the GFDI installation manual.

Any listing of the GFDI breakers currently available from Outback.



Am I not looking in the right place?



I hope the above discussion helps you detail-oriented PV designers out
there.  I am hoping Lones can provide some input on these subjects.  Lones
has been very on top of his responsibilities and I am grateful to him.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Tuss, Lones
*Sent:* Friday, January 21, 2022 9:39 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Mixing Outback FM100 CC with Fm80 or 60.



Ahh the can of worms get opened.

In our conversation Willian brought up the same points.

All true, but the white paper was required by legal (CYA).

I think getting the new unit listed also came into play.







*From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On Behalf
Of *Maverick Brown
*Sent:* Friday, January 21, 2022 9:29 AM
*To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] Mixing Outback FM100 CC with Fm80 or 60.



*CAUTION:* This email originated from outside of the Company. Do not click
links or open attachments unless you recognize the sender and know the
content is safe.



Using that logic, wouldn’t the inverters and batteries also be exposed to
300Vdc? And the MX60 would also be at risk for exposing the inverters and
batteries to 150Vdc under similar failures?



If that’s the only limiting factor, I’d like to take back a couple AC
Coupling arrangements I have made for past Radian expansions. ;-)

Maverick Brown
Off-Grid Solar Commander since 2006
*Maverick Solar Enterprises, Inc.*

* • Solar Commander Remote Power*


* • SunFlow Systems Cathodic Protection *maverick at mavericksolar.com
512-460-9825





On Jan 21, 2022, at 11:15 AM, Tuss, Lones <lones.tuss at enersys.com> wrote:



Hi William

Thank you for taking my call.

I believe the reason we do not recommend mixing the FM100 and the fM60/80
is.

If the FM100 were to short out pv input to output you could expose the 150
volt rated dc breakers on the

FM60/80 to 300 vdc.







*From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On Behalf
Of *William Miller
*Sent:* Thursday, January 20, 2022 10:54 PM
*To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
*Subject:* [RE-wrenches] Mixing Outback FM100 CC with Fm80 or 60.



*CAUTION:* This email originated from outside of the Company. Do not click
links or open attachments unless you recognize the sender and know the
content is safe.



Friends:



I am sure many of you are familiar with the somewhat new Outback FM100
charge controller.  It allows PV input at up to 300 volts and battery feed
at up to 100 amps.  It has a built in GFDI fuse, much like the old XW--now
branded I think Conextant-- charge controller.



Outback recommends against installing an FM 100 in an installation with
FM60s or FM 80s.  Here is the tech note
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-4df62a772b14c6eb&q=1&e=d5f26548-4212-48c3-91e9-e4b3dde4c8e7&u=https%3A%2F%2Foutbackpower.com%2Fdownloads%2Fdocuments%2Fappnotes%2Ffm100_fm80_app_note.pdf>
that gives that recommendation.  Below is one paragraph from that tech note.



*There is little benefit to mixing an FM100 with an FM60/80. If
circumstances require it, this application*

*note will explore an option.*



Note the language is pretty dang squirrely.  Let’s parse the above
paragraph:



Sentence 1:  I submit there may be many scenarios where there is
significant benefit:  Like if you already have an FM60/80 and you want to
add more PV and you want to enjoy the benefits of an FM100, such as higher
input voltage or higher output amperage, and not have to fork out an extra
$1000 to replace a working FM60/80.  Or you installing more than one PV
array,  one array nearby and/or smaller and one further away or larger, and
you don’t want to spend close to $1,000 to charge control the nearer array.



Sentence 2:  They are offering “an option,” not the only option.  I believe
there are multiple options. In a mixed installation, the FM100 can rely on
its internal GFDI fuse and the FM60 or 80 can rely on the old familiar GFDI
breaker with the 1 or 0.5 amp pole connected between the negative and
equipment grounding system.  Alternatively, Midnite sells a 300 volt rated,
multi-pole GFDI breaker that could be shared by an FM100 and an F60/80.  It
says right in the FM100 manual that you can use external GFDI devices (page
14).



I am not at all clear as to what problem there is to mixing the two
generations of charge controllers.  I reviewed the NEC.  There is no
indication that thou shall not mix GFDI styles.



If anyone has a definitive reason why or why not to mix these models of
Outback charge controllers, I would be most interested.



Most Sincerely,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-18562c478088e59c&q=1&e=d5f26548-4212-48c3-91e9-e4b3dde4c8e7&u=http%3A%2F%2Fwww.millersolar.com%2F>

CA Lic. 773985







This email and any attachments may contain confidential information that is
intended only for the recipient(s). If you have received this email in
error, please notify the sender and delete it from your system. Any views
or opinions presented in this email are solely those of the author and do
not necessarily represent those of the company or its affiliates. This
email does not constitute an agreement to conduct transactions by
electronic means and does not create any legally binding contract or
enforceable obligation in the absence of a fully signed written contract.
The recipient should check this email and any attachments for viruses. The
company accepts no liability for any loss or damage caused by software
viruses. If you are the intended recipient and you do not wish to receive
similar email(s) from us in the future then please notify the sender.
Please consider the environment before printing.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=http%3A%2F%2Fre-wrenches.org%2F>

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-e399d9bb5547f820&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org
<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=1caf6717-512c-4510-9f48-73a1c0b5d05d&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>



This email and any attachments may contain confidential information that is
intended only for the recipient(s). If you have received this email in
error, please notify the sender and delete it from your system. Any views
or opinions presented in this email are solely those of the author and do
not necessarily represent those of the company or its affiliates. This
email does not constitute an agreement to conduct transactions by
electronic means and does not create any legally binding contract or
enforceable obligation in the absence of a fully signed written contract.
The recipient should check this email and any attachments for viruses. The
company accepts no liability for any loss or damage caused by software
viruses. If you are the intended recipient and you do not wish to receive
similar email(s) from us in the future then please notify the sender.
Please consider the environment before printing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220125/d7b716c1/attachment.htm>


More information about the RE-Wrenches mailing list