[RE-wrenches] Sol-Ark AC Coupling Issues
Jeff Clearwater
jeffc at villagepowerdesign.com
Wed Jan 19 22:05:45 EST 2022
Yes what Jay said - need a block diagram with available power flows on
this one. If you've been working with Sol-Ark you probably covered the
basics but just for the rest of us to be assured:
I assume:
1) you are using the Radian only as an AC Grid-Tie inverter - no
batteries on it?
2) that you are aware that the AC Coupled wattage plus the DC wattage on
the Sol-Ark's MPPTs must be within the total allowed for solar generation
3) that you have the AC Coupled output of the Radian connected to the
GEN breaker of the Sol-Ark
4) that you have the software set for the GEN breaker to be AC Coupled
and have checked all other software items with Sol-Ark needed for AC
coupling
just as a starting base for us to understand what may be happening.
And some of the techs at Sol-Ark are in training - have you talked to
the tech lead, Dustin Douglas? He's the official Sol-Ark rep on this
list but I just saw him at InterSolar and he said he has been just too
busy to chime in here much. I'm scheduled to speak with him soon - I'll
see if he can find the time if he hasn't already talked to you.
Best,
Jeff
> Vince McClellan <mailto:vince at solarenergydesign.com>
> January 19, 2022 at 3:15 PM
> Is anyone on the list familiar with AC coupling Sol-Ark inverters?
> We haven't been able to AC couple an existing Outback Radian system to
> a new system that we built with 3, Sol-Ark 12K inverters and 3, Blue
> Ion batteries. Each time we have tested the system the Sol-Ark
> inverters accept the power from the Radian inverter until we turn on
> the DC power from the new solar array to the Sol-Ark inverters. As
> soon as there is significant DC power coming from the solar array the
> Sol-Ark inverters freq-watt turns on for a brief second and
> disconnects the Radian inverter even when the Blue Ion batteries are
> below the programmed state of charge threshold. If we don't turn on
> the DC power from the new solar array the Radian will connect and stay
> connected.
>
> We have been working with Sol-Ark for several months now to get this
> system to accept the incoming power from the Radian without freq-watt
> kicking in on the Sol-Ark inverters and disconnecting the Radian
> inverter. Sol-Ark has sent two software revisions to the Sol-Ark
> inverters and we are still experiencing the same problem.
>
> Can anyone think of what we might be missing and where to direct our
> troubleshooting efforts next?
>
> Thanks,
>
> Vince McClellan
> Energy Design
> NABCEP PV Installation Professional
> p. (541) 485-8122 <tel:%28541%29%20485-8122> f. (541) 338-8202
> <tel:%28541%29%20338-8202>
>
> If you have received this email and are not the intended recipient
> please delete this email. Copying, or using any part, content, or
> attachment of this email is strictly prohibited.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220119/499e7f42/attachment.htm>
More information about the RE-Wrenches
mailing list