[RE-wrenches] Transmitting 15kW 3600ft Off Grid.
Kent
kent at coveoregon.com
Mon Jan 10 12:35:25 EST 2022
The decision to use transformers, to step the voltage up and down,
rather than larger wire for a long circuit is more complicated than
simply comparing the cost of the wire to the cost of transformers and
smaller wire. Even with good toroidal transformers, the transformer pair
is adding about 10% loss in the system. And while the transformer
hysteresis losses may be a less than 1% of the transformer capacity,
they are 24/7 independent of the load. The supply side costs to provide
for the lost energy in the transformers needs to be considered too.
Kent Osterberg
Blue Mountain Solar
On 1/10/2022 6:24 AM, Hilton Dier wrote:
> So you have a client with clever ideas - my deepest sympathies. The five most frightening words from a client are “I am a retired engineer.”
>
> DC transmission is theoretically more efficient due to the surface conduction effects of AC. However, this is only true in a practical sense at utility/megawatt scale. At residential scale you will have losses in the electronics at either end that will negate the wire savings.
>
> Get some toroidal transformers and go to 480 and back. Fat wire is kind of expensive, but really it’s the trench (and these days, pvc conduit) that cost the money. Fat wire in conduit is solid state and will never blow a capacitor. Transformers, if not overloaded, last.
>
> On that last point, 2x oversize the transformers for the load. There will be “mission creep” while you aren’t looking. “Oh, we didn’t think that half a dozen 1500 watt resistance heaters scattered around would make any difference.”
>
> Good luck.
>
> Hilton Dier III
> Renewable Energy Design