[RE-wrenches] Transmitting 15kW 3600ft Off Grid.

Ray ray at solarray.com
Mon Jan 10 12:06:03 EST 2022


That's a long enough run that you really need to weigh the cost of a 
separate system.  I'm not seeing the advantages of keeping a single 
system for the whole island.

Ray Walters
Remote Solar
303 505-8760

On 1/10/22 9:43 AM, Chris Mason wrote:
> I would use a 6,600V single phase outdoor pad mounted transformer pair 
> and deep bury a single #2 direct burial cable. Easy and quick.
>
> On Mon, Jan 10, 2022 at 7:34 AM Foxfire Energy 
> <dan at foxfire-energy.com> wrote:
>
>     Hi Guys, Got a good one for you.. We were tasked to refurbish a
>     Stand Alone (aka Off Grid) power system on a 100 acre private
>     resort island off the New England coast a few years back.. The
>     system has a 12kW(AC)/ 48VDC power center (@120/240VAC) with a
>     10kW Bergey wind turbine, 3kW of Solar and a 12kW Diesel
>     Generator.. It currently powers two main lodges and 10 private
>     cabins.. The system was never installed properly and had
>     significant damage when we got there (no system ground, evidence
>     of several lightening strikes, open/corroded connections, and poor
>     workmanship in general)
>     The new owners want to build a third lodge at the other end of the
>     island.. Some 3600ft away, and want to feed full power from the
>     existing system to the new lodge.. Thing is, the new owner is
>     pretty brainy (keeps me on my toes).. My first thought was to bump
>     the 120/240VAC up to 480VAC and send it on like 4/0AL and back
>     down to 120/240VAC at the new lodge (we've done it before).. The
>     new owner wants to launder the AC to DC and back for
>     transmission.. Says DC for transmission is the new Cats Pajamas
>     because of the efficiency.. News to me.. Anyone have experience
>     with DC for transmission? Again.. I'm shooting for 15kW (including
>     25% for continuous duty), 3600ft, 600V wire (but could go with a
>     different wire) and a line loss under 5%. TIA db
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     Pay optional member dues here: http://re-wrenches.org
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     There are two list archives for searching. When one doesn't work,
>     try the other:
>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     http://www.re-wrenches.org/etiquette.htm
>
>     Check out or update participant bios:
>     http://www.members.re-wrenches.org
>
>
>
> -- 
> Chris Mason
> Solar systems designer
> Generac Generators Industrial technician
>
> Comet Systems Ltd DBA Comet Solar
> Anguilla Cell  264.235.5670
> WhatsApp 264.235.5670
> Skype: netconcepts
> www.cometsolar.com <http://www.cometenergysystems.com/>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220110/fe380985/attachment.htm>


More information about the RE-Wrenches mailing list