[RE-wrenches] Transmitting 15kW 3600ft Off Grid.
Ray
ray at solarray.com
Mon Jan 10 12:06:03 EST 2022
That's a long enough run that you really need to weigh the cost of a
separate system. I'm not seeing the advantages of keeping a single
system for the whole island.
Ray Walters
Remote Solar
303 505-8760
On 1/10/22 9:43 AM, Chris Mason wrote:
> I would use a 6,600V single phase outdoor pad mounted transformer pair
> and deep bury a single #2 direct burial cable. Easy and quick.
>
> On Mon, Jan 10, 2022 at 7:34 AM Foxfire Energy
> <dan at foxfire-energy.com> wrote:
>
> Hi Guys, Got a good one for you.. We were tasked to refurbish a
> Stand Alone (aka Off Grid) power system on a 100 acre private
> resort island off the New England coast a few years back.. The
> system has a 12kW(AC)/ 48VDC power center (@120/240VAC) with a
> 10kW Bergey wind turbine, 3kW of Solar and a 12kW Diesel
> Generator.. It currently powers two main lodges and 10 private
> cabins.. The system was never installed properly and had
> significant damage when we got there (no system ground, evidence
> of several lightening strikes, open/corroded connections, and poor
> workmanship in general)
> The new owners want to build a third lodge at the other end of the
> island.. Some 3600ft away, and want to feed full power from the
> existing system to the new lodge.. Thing is, the new owner is
> pretty brainy (keeps me on my toes).. My first thought was to bump
> the 120/240VAC up to 480VAC and send it on like 4/0AL and back
> down to 120/240VAC at the new lodge (we've done it before).. The
> new owner wants to launder the AC to DC and back for
> transmission.. Says DC for transmission is the new Cats Pajamas
> because of the efficiency.. News to me.. Anyone have experience
> with DC for transmission? Again.. I'm shooting for 15kW (including
> 25% for continuous duty), 3600ft, 600V wire (but could go with a
> different wire) and a line loss under 5%. TIA db
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> --
> Chris Mason
> Solar systems designer
> Generac Generators Industrial technician
>
> Comet Systems Ltd DBA Comet Solar
> Anguilla Cell 264.235.5670
> WhatsApp 264.235.5670
> Skype: netconcepts
> www.cometsolar.com <http://www.cometenergysystems.com/>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220110/fe380985/attachment.htm>
More information about the RE-Wrenches
mailing list