[RE-wrenches] Outback Mate 3s AGS problems

Dan Fink danbob88 at gmail.com
Fri Jan 7 17:02:36 EST 2022


Wrenches; Having a frustrating problem here with a Mate 3s and 2-wire AGS.
The generator starts and stops fine from the Mate 3 AND via Optics RE from
my smartphone,  but will not autostart by either SOC or Voltage. It is
wired to use the inverter (VFXR 3524A) 12vdc aux output to an Outback relay
board in the gen  as I've had issues in the past using the FNDC relay (as I
think other Wrenches have too). The Mate 3s AGS is set for the Inverter
port (4).

In the past on other Mate 3s systems, I seem to remember always making sure
the Inverter AUX relay mode is set to REMOTE to allow the Mate 3s to
control the gen instead of the very limited GEN FAULT AGS setting in the
inverter. But when I pull that up both via Optics and the Mate 3s itself,
there IS no "remote" option anymore. The Mate3s firmware was updated last
month to the latest version.

If the REMOTE setting for the VFXR inverter no longer exists, what do I set
the inverter AUX relay for to enable the Mate 3s advanced AGS to assume
control? Or should I delegate AGS responsibilities to one of the FX PV
controllers , just re-routing the 2 genstart wires? Not to the FNDC I
assume because of those past problems.

I'm pretty sure this issue has to be conflicting AGS instructions from
different components, as sitting here at the kitchen table at the client's
off grid house I can start and stop the gen from my phone!

Thanks for any suggestions!

Dan Fink
Buckville Energy Consulting LLC
970-672-4342