[RE-wrenches] Large lithium chargers

Nick A Lucchese lucchesesolar at me.com
Fri Dec 3 03:35:49 EST 2021


Hello Jay,

This was my same dilemma I posted about recently although not 208. Have you considered SMA Islands in a Multicluster system? I did one last year and other than tracking down a mis-wire on the CT’s in the Multicluster box it’s been working extremely well. Do you know what brand of batteries yet? Blue Ions are closed loop communications with the Islands now so it works beautifully. There’s some reasonable deals on many of the Sunny Island 6048’s right now from the DC Solar auctions too. One of the last ones just ended yesterday actually. It would likely be easy to find many at 25-33% less than the old distributor’s pricing.

Would love to hear what you decide to do with this. Best of luck, Nick




> On Dec 2, 2021, at 7:53 AM, Jay <jay.peltz at gmail.com> wrote:
> 
> Hi all
> 
> Sorry I guess I didn’t explain the clients wants well enough
> 
> 1. 90-100kwh+ 48 vdc lithium battery 
> 2. 208 3 phase AC generator powering 48v nominal battery chargers.
> 208-3phase as that is the house/EE design voltage. 
> 3. AC generator because it’s back up if the inverters fail, so no DC generator. 
> 4. Client doesn’t want any drop outs or have to reset clocks etc during generator/inverter- charging/switchover.
> 5. Inverter size is not decided yet, probably 40-80kw. 
> 6.  Generator size isn’t specified yet, but given the loads 60-125kw probably. 
> Size would be based on battery charging or max ac load which ever is larger. 
> 
> That leads me external chargers. 
> 
> I’m looking for large programmable battery chargers for lithium batteries powered from a 208-3phase ac generator in the 60-125 kw size range. 
> 
> Thanks
> 
> Jay
> 