[RE-wrenches] Outback MX-60 - Li-ion charging
bob at midnitesolar.com
bob at midnitesolar.com
Wed Dec 1 15:24:38 EST 2021
Thanks Larry.
The information to stop when absorb voltage was reached is like, 10 or
more years old and so I
don't know if that voltage reach and stop charging algorithm is still
used by any BMS's.
This is probably why we had to add a logic input to tell the controller
to stop charging from the BMS.
After the 0.3 hours at Absorb for balancing (which makes perfect sense
for a BMS), does the MX/FM then
go to float at 3.65V per cell after that ?
Does your systems just restart a new bulk/absorb cycle the next morning
or do you also do a Re-Bulk if
or when battery voltage falls below a certain point ?
Also, listening (reading) chat here on what might be needed that may not
have been addressed by
Li battery, BMS and/or charge controller manufacturers.
Thanks,
boB
On 12/1/2021 12:03 PM, larrycrutcher wrote:
> If you stop charging a Li-ion battery when the CV (absorb voltage) is
> reached, you may reduce or stop the needed cell balancing time. We
> have had customers develop unbalanced series cells from continuous
> undercharging. Because of internal cell resistance, one cell will
> always reach saturation before others in the group. This can happen at
> less than 1mv difference. The more unbalanced a group of series cells
> are, the sooner one cells voltage will spike causing over voltage
> events at a lower terminal voltage.
>
> Our Li batteries (Elite Power Solutions-GBS and LiFeBlue) can be held
> at 3.65Vpc continuously, no problems. We have customers using both MX
> and FM controllers for 8 years now. Our recommended setting for the
> Absorb timer is 0.3 hours. This allows for cell balancing and for the
> capacity meter to recalibrate. Some chargers will stay at CV for
> several hours. No problems doing this either as long as cell voltage
> is lower than 3.8V (LFP chem.).
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> On Dec 1, 2021, at 9:38 AM, bob at midnitesolar.com wrote:
>
>
>
> Depends on the requirement for the BMS.
>
> Usually, but not 100% always, the requirement is to get the voltage up
> to "absorb" and then stop charging.
>
> Just set the min and max times very low, like 1 minute and that
> should satisfy that one.
>
> I do not remember if the MX60 had a Re-Bulk setting but I think it did ?
>
> The MX did not have a logic input for turning it on and off of
> course. OB had a communications
> device that converted their communications protocol to Modbus or
> Ethernet I think it was which
> may (or may not) be able to make it work.
>
> Could always buy something newer and keep the MX60 as a spare.
>
> boB
>
>
>
> On 12/1/2021 9:10 AM, frenergy wrote:
>>
>> boB,
>>
>> Interesting...Sounds like this is not a candidate for
>> L-ion batteries.
>>
>> Bill
>>
>> On 11/30/2021 10:47 PM, bob at midnitesolar.com wrote:
>>>
>>> Hi Bill....
>>>
>>> As I remember, the min is of course... Minimum time in Absorb.
>>>
>>> Max is maximum time in absorb but depended on how long it took to
>>> get from Bulk MPPT to that Absorb voltage.
>>>
>>> So if it took 3 hours to get to Absorb that morning and you had t
>>> set for Max 2 hours, it would Absorb for 2 hours.
>>>
>>> If it only took 1 and 1/2 hours to reach Absorb voltage, the MX60
>>> would Absorb for 1 and 1/2 hours.
>>>
>>> It worked "OK" but these days I would probably just set it for min
>>> of some 2 or 3 hours and then a max could be the same
>>> time or longer for FLA batteries.
>>>
>>> boB
>>>
>>>
>>>
>>> On 11/30/2021 7:16 PM, frenergy wrote:
>>>>
>>>> Yes, the old one, not the FM. This oldie had an interesting way to
>>>> set the absorption time. You would set the "min" time (in minutes)
>>>> and you would set the "max" time (in hours, you have to set it to
>>>> 1,2,3 or 4 hours).
>>>>
>>>> I need to know if I set the "min" to 10 minutes and the
>>>> "max" time to one hour or two or three or four, how long will it
>>>> stay in absorb?
>>>>
>>>> I called Outback and Megan there didn't know how this
>>>> old fart works, apparently tech support isn't supporting us their
>>>> old relics.
>>>>
>>>> Bill
>>>>
>>>> Feather River Solar Electric
>>>> Bill Battagin, Owner
>>>> 4291 Nelson St.
>>>> Taylorsville, CA 95983
>>>> 530.284.7849
>>>> CA Lic 874049
>>>> solar powered since 1982
>>>>
>>>>
>>
>>
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>
>> Virus-free. www.avast.com
>> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
>>
>>
>> <x-msg://68/#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211201/d9d23d37/attachment.htm>
More information about the RE-Wrenches
mailing list