Yesterday, I was able to upload firmware to the Mate 3s, and the GS4048
and program it for AC coupling. I did not realize a firmware update
would shut down the inverter (makes sense that it does), so that was a
bit of a surprise, but all in all it went very well. The Mate3s
firmware was out of date by almost a year, and that did not allow the
inverter firmware and its AC coupling capability to be set. Once I
update the Mate3s, I was able to specify AC coupling. Thanks for all the
suggestions and I know I will be able to use them in other situations.
Chris
On 11/24/2021 2:39 PM, Christopher Warfel wrote:
>
> Thanks to everyone, the setting I had said AC coupling No. I did not
> realize that a firmware upgrade could enable that. I think it is best
> to try frequency shift for this particular case. Thanks again to
> everyone. Chris
>
> On 11/24/2021 12:38 PM, Tuss, Lones wrote:
>>
>> Hello Chris
>>
>> Sorry for the slow response I foolishly took a couple of days of
>> vacation.
>>
>> I see this system is on Optics. The GS4048A inverter can do AC
>> Coupling with frequency shift. It will need to be upgraded from the
>> current rev of 001.006.063 to 001.007.070 below is a link to
>> that firmware.
>>
>> https://outbackpower.com/resources-mobile/technical-support/firmware-updates/item/radian-series-firmware-updates
>>
>> Once the new firmware is installed will need to change the default
>> Installer password of 1732 to a different 4 digit number after doing
>> so In the inverter you can go to the menu and enable AC Coupling.
>>
>> Below are instructions for changing the default Installer Password.
>>
>> https://outbackpower.com/downloads/documents/system_management/mate3s/mate3s_programmingguide_web.pdf
>>
>> please see S-16 in the manual above.
>>
>> Below is a link to the AC Coupling App Note
>>
>> https://outbackpower.com/downloads/documents/appnotes/ac_coupling_radian.pdf
>>
>> I too speak English as my native foreign language below is a link to
>>
>> Fowlers Modern English Usage
>>
>> It has helped me to spoke more lucidly and communicate more better.
>>
>> https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8
>> <https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8>
>>
>> Thanks for using OutBack
>>
>> Chris you have my # if you have questions.
>>
>> Have a good Thanksgiving and Stay Safe.
>>
>> Take Care All
>>
>> *From:* RE-wrenches
>> <re-wrenches-bounces at lists.re-wrenches001.007.070.org> *On Behalf Of
>> *Christopher Warfel
>> *Sent:* Tuesday, November 23, 2021 9:40 AM
>> *To:* August Goers <august at luminalt.com>; RE-wrenches
>> <re-wrenches at lists.re-wrenches.org>
>> *Subject:* Re: [RE-wrenches] Rapid Shutdown Control for a System for
>> a Multimode System Adding an Array to a Subpanel in Garage
>>
>>
>>
>>
>> *CAUTION:*This email originated from outside of the Company. Do not
>> click links or open attachments unless you recognize the sender and
>> know the content is safe.
>>
>> It was tough for me to figure out how to write my email and not make
>> it confusing.
>>
>> What I am worried about is the microinverter system operating when
>> the utility goes down and the microinverters continuing to operate
>> and charge the batteries as a load. I need to disconnect the
>> microinverter circuit only when the batteries are fully charged in
>> grid isolated mode. All the ways I can think of that would normally
>> work to deenergize the microinverters automatically based upon
>> battery voltage won't work. I can submit a drawing if that would
>> help. I am trying not to run another conductor circuit from the house
>> to the garage. I realize that would solve the problem, but it is an
>> expensive solution. English is my foreign native language.
>>
>> On 11/23/2021 10:39 AM, August Goers wrote:
>>
>> Hi Chris - If I'm following you right, you have a PV system on a
>> detached garage that ties into a backup subpanel also in the
>> garage? The code only requires the RSID (rapid shutdown
>> initiation device) to be on the exterior of the building. Would
>> it work to put the RSID on the garage exterior? You could route
>> your PV circuits to a switch or switches on the exterior of the
>> garage on the way down to the sub it ties into. You could also
>> use a shunt trip breaker(s) for the PV circuit(s). If for some
>> reason you need to have the RSID on the main house, it gets
>> trickier. Might need to trench?
>>
>> August
>>
>> Luminalt
>>
>> On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel
>> <cwarfel at entech-engineering.com> wrote:
>>
>> I would appreciate ideas on how to shut down a proposed
>> microinverter system on a garage that is 100% serviced by an
>> Outback Radian multimode system in the main building that has
>> the garage on the back up service panel in the main building.
>>
>> Garage has a MLO subpanel that is connected to the multimode
>> back up service panel that is in the main building.
>>
>> If grid goes down, we need to disconnect the microinverter
>> array so it does not overcharge the battery system. If we use
>> the battery voltage relay, we will take out all the garage
>> circuits, which would disable its heating system, etc. We
>> just want to disconnect the microinverter circuit in the
>> garage subpanel.
>>
>> Does anyone know of a product that could do this. I would
>> imagine a transmitter, or perhaps something else besides a
>> microinverter array?
>>
>> Thanks for any help. Chris
>>
>> --
>>
>> Christopher Warfel
>> ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>> 401-466-8978
>> <https://protect2.fireeye.com/v1/url?k=b5daa01b-ea4198e0-b5d9a990-861a44d80f79-8d6d4e72be5eadfb&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>> <https://protect2.fireeye.com/v1/url?k=b8b7ead7-e72cd22c-b8b4e35c-861a44d80f79-a7380300fe73d86f&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fre-wrenches.org%2F>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://protect2.fireeye.com/v1/url?k=c48af253-9b11caa8-c489fbd8-861a44d80f79-4310075dc69a7106&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>
>>
>> There are two list archives for searching. When one doesn't
>> work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://protect2.fireeye.com/v1/url?k=7727c68b-28bcfe70-7724cf00-861a44d80f79-cea6b969f07330fd&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://protect2.fireeye.com/v1/url?k=725c0d09-2dc735f2-725f0482-861a44d80f79-954c92e3067c4765&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://protect2.fireeye.com/v1/url?k=94b19eb0-cb2aa64b-94b2973b-861a44d80f79-60c1cb03e533eee0&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>
>>
>> --
>>
>> Christopher Warfel
>> ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>> 401-466-8978
>> <https://protect2.fireeye.com/v1/url?k=29e1c951-767af1aa-29e2c0da-861a44d80f79-821d84c651c96860&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
>>
>>
>>
>> This email and any attachments may contain confidential information
>> that is intended only for the recipient(s). If you have received this
>> email in error, please notify the sender and delete it from your
>> system. Any views or opinions presented in this email are solely
>> those of the author and do not necessarily represent those of the
>> company or its affiliates. This email does not constitute an
>> agreement to conduct transactions by electronic means and does not
>> create any legally binding contract or enforceable obligation in the
>> absence of a fully signed written contract. The recipient should
>> check this email and any attachments for viruses. The company accepts
>> no liability for any loss or damage caused by software viruses. If
>> you are the intended recipient and you do not wish to receive similar
>> email(s) from us in the future then please notify the sender. Please
>> consider the environment before printing.
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211201/86b77e73/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211201/86b77e73/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211201/86b77e73/attachment-0001.jpg>
More information about the RE-Wrenches
mailing list