Thanks to everyone, the setting I had said AC coupling No. I did not 
realize that a firmware upgrade could enable that.  I think it is best 
to try frequency shift for this particular case.  Thanks again to 
everyone.  Chris

On 11/24/2021 12:38 PM, Tuss, Lones wrote:
>
> Hello Chris
>
> Sorry for the slow response I foolishly took a couple of days of 
> vacation.
>
> I see this system is on Optics. The GS4048A inverter can do AC 
> Coupling with frequency shift. It will need to be upgraded from the 
> current rev of 001.006.063    to  001.007.070 below is a link to that 
> firmware.
>
> https://outbackpower.com/resources-mobile/technical-support/firmware-updates/item/radian-series-firmware-updates
>
> Once the new firmware is installed  will need to change the default 
>  Installer password of 1732 to a different 4 digit number after doing 
> so In the inverter you can go to the menu and enable AC Coupling.
>
> Below are instructions for changing the default Installer Password.
>
> https://outbackpower.com/downloads/documents/system_management/mate3s/mate3s_programmingguide_web.pdf
>
> please see S-16 in the manual above.
>
> Below is a link to the AC Coupling App Note
>
> https://outbackpower.com/downloads/documents/appnotes/ac_coupling_radian.pdf
>
> I too speak English as my native foreign language below is a link to
>
> Fowlers Modern English Usage
>
> It has helped me to spoke more lucidly and communicate more better.
>
> https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8 
> <https://www.amazon.com/s?k=fowlers+modern+english+usage&crid=3AUWAC3TGDBWQ&sprefix=fowlers+%2Caps%2C277&ref=nb_sb_ss_ts-doa-p_2_8>
>
> Thanks for using OutBack
>
> Chris you have my #  if you have questions.
>
> Have a good Thanksgiving  and Stay Safe.
>
> Take Care All
>
> *From:* RE-wrenches 
> <re-wrenches-bounces at lists.re-wrenches001.007.070.org> *On Behalf Of 
> *Christopher Warfel
> *Sent:* Tuesday, November 23, 2021 9:40 AM
> *To:* August Goers <august at luminalt.com>; RE-wrenches 
> <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Rapid Shutdown Control for a System for a 
> Multimode System Adding an Array to a Subpanel in Garage
>
>
> 	
>
> *CAUTION:*This email originated from outside of the Company. Do not 
> click links or open attachments unless you recognize the sender and 
> know the content is safe.
>
> It was tough for me to figure out how to write my email and not make 
> it confusing.
>
> What I am worried about is the microinverter system operating when the 
> utility goes down and the microinverters continuing to operate and 
> charge the batteries as a load.  I need to disconnect the 
> microinverter circuit only when the batteries are fully charged in 
> grid isolated mode.  All the ways I can think of that would normally 
> work to deenergize the microinverters automatically based upon battery 
> voltage won't work.  I can submit a drawing if that would help. I am 
> trying not to run another conductor circuit from the house to the 
> garage.  I realize that would solve the problem, but it is an 
> expensive solution.  English is my foreign native language.
>
> On 11/23/2021 10:39 AM, August Goers wrote:
>
>     Hi Chris - If I'm following you right, you have a PV system on a
>     detached garage that ties into a backup subpanel also in the
>     garage? The code only requires the RSID (rapid shutdown
>     initiation device) to be on the exterior of the building. Would it
>     work to put the RSID on the garage exterior? You could route your
>     PV circuits to a switch or switches on the exterior of the garage
>     on the way down to the sub it ties into. You could also use a
>     shunt trip breaker(s) for the PV circuit(s). If for some reason
>     you need to have the RSID on the main house, it gets trickier.
>     Might need to trench?
>
>     August
>
>     Luminalt
>
>     On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel
>     <cwarfel at entech-engineering.com> wrote:
>
>         I would appreciate ideas on how to shut down a proposed
>         microinverter system on a garage that is 100% serviced by an
>         Outback Radian multimode system in the main building that has
>         the garage on the back up service panel in the main building.
>
>         Garage has a MLO subpanel that is connected to the multimode
>         back up service panel that is in the main building.
>
>         If grid goes down, we need to disconnect the microinverter
>         array so it does not overcharge the battery system. If we use
>         the battery voltage relay, we will take out all the garage
>         circuits, which would disable its heating system, etc. We just
>         want to disconnect the microinverter circuit in the garage
>         subpanel.
>
>         Does anyone know of a product that could do this. I would
>         imagine a transmitter, or perhaps something else besides a
>         microinverter array?
>
>         Thanks for any help. Chris
>
>         -- 
>
>         Christopher Warfel
>                          ENTECH Engineering, Inc.
>         PO Box 871, Block Island, RI 02807
>                             401-466-8978
>         <https://protect2.fireeye.com/v1/url?k=b5daa01b-ea4198e0-b5d9a990-861a44d80f79-8d6d4e72be5eadfb&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         Pay optional member dues here: http://re-wrenches.org
>         <https://protect2.fireeye.com/v1/url?k=b8b7ead7-e72cd22c-b8b4e35c-861a44d80f79-a7380300fe73d86f&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fre-wrenches.org%2F>
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>         <https://protect2.fireeye.com/v1/url?k=c48af253-9b11caa8-c489fbd8-861a44d80f79-4310075dc69a7106&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>
>
>         There are two list archives for searching. When one doesn't
>         work, try the other:
>         https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>         http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>         <https://protect2.fireeye.com/v1/url?k=7727c68b-28bcfe70-7724cf00-861a44d80f79-cea6b969f07330fd&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>
>
>         List rules & etiquette:
>         http://www.re-wrenches.org/etiquette.htm
>         <https://protect2.fireeye.com/v1/url?k=725c0d09-2dc735f2-725f0482-861a44d80f79-954c92e3067c4765&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>
>
>         Check out or update participant bios:
>         http://www.members.re-wrenches.org
>         <https://protect2.fireeye.com/v1/url?k=94b19eb0-cb2aa64b-94b2973b-861a44d80f79-60c1cb03e533eee0&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>
>
> -- 
>
>                     Christopher Warfel
>                  ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
>             401-466-8978
> <https://protect2.fireeye.com/v1/url?k=29e1c951-767af1aa-29e2c0da-861a44d80f79-821d84c651c96860&q=1&e=419d5d1e-c0ac-4d3f-ad1a-8cfab76f8c9b&u=http%3A%2F%2Fentech-engineering.com%2F>
>
>
>
> This email and any attachments may contain confidential information 
> that is intended only for the recipient(s). If you have received this 
> email in error, please notify the sender and delete it from your 
> system. Any views or opinions presented in this email are solely those 
> of the author and do not necessarily represent those of the company or 
> its affiliates. This email does not constitute an agreement to conduct 
> transactions by electronic means and does not create any legally 
> binding contract or enforceable obligation in the absence of a fully 
> signed written contract. The recipient should check this email and any 
> attachments for viruses. The company accepts no liability for any loss 
> or damage caused by software viruses. If you are the intended 
> recipient and you do not wish to receive similar email(s) from us in 
> the future then please notify the sender. Please consider the 
> environment before printing. 
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211124/0a8b4d4c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211124/0a8b4d4c/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211124/0a8b4d4c/attachment-0001.jpg>


More information about the RE-Wrenches mailing list