Hi Chris - If I'm following you right, you have a PV system on a detached
garage that ties into a backup subpanel also in the garage? The code only
requires the RSID (rapid shutdown initiation device) to be on the exterior
of the building. Would it work to put the RSID on the garage exterior? You
could route your PV circuits to a switch or switches on the exterior of the
garage on the way down to the sub it ties into. You could also use a shunt
trip breaker(s) for the PV circuit(s). If for some reason you need to have
the RSID on the main house, it gets trickier. Might need to trench?
August
Luminalt
On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel <
cwarfel at entech-engineering.com> wrote:
> I would appreciate ideas on how to shut down a proposed microinverter
> system on a garage that is 100% serviced by an Outback Radian multimode
> system in the main building that has the garage on the back up service
> panel in the main building.
>
> Garage has a MLO subpanel that is connected to the multimode back up
> service panel that is in the main building.
>
> If grid goes down, we need to disconnect the microinverter array so it
> does not overcharge the battery system. If we use the battery voltage
> relay, we will take out all the garage circuits, which would disable its
> heating system, etc. We just want to disconnect the microinverter circuit
> in the garage subpanel.
>
> Does anyone know of a product that could do this. I would imagine a
> transmitter, or perhaps something else besides a microinverter array?
>
>
> Thanks for any help. Chris
>
>
>
>
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211123/98af7536/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211123/98af7536/attachment.jpg>
More information about the RE-Wrenches
mailing list