[RE-wrenches] outback skybox remote power off

Bradley Bassett bbassett2 at gmail.com
Sun Nov 7 14:41:33 EST 2021


If you open terminals 4 and 12 it will turn off the Skybox, both PV input
and AC as far as I know. Terminals 5 and 13 then will open on RSD to send a
signal to whatever other devices need RSD.

Brad

On Sun, Nov 7, 2021 at 9:34 AM Kirk Herander <kirkh at vermont.solar> wrote:

> I just installed one of these in a commercial building. I have a Solaredge
> inverter AC coupled through it. The AHJ wants me to install a first
> responder EPO switch outside to shut down the AC output of the
> inverter(which will totally kill all AC sources along with the normal AC
> utility/inverter disco). The skybox does not have a simple on/off
> connection for remote control of the inverter from what I see in the
> manual.
>
> I can use the 12v out aux contact to control a power relay to shut the
> inverter AC off manually. Any other way I can accomplish this? Thanks.
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 30th Anniversary 1991-2021!!*
>
> *www.vermont.solar*
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211107/3c63ab16/attachment.htm>


More information about the RE-Wrenches mailing list