[RE-wrenches] Harris lithium battery as drop-in replacement for Outback RE2200 AGM?
scot.arey at solarcentex.com
scot.arey at solarcentex.com
Thu Nov 4 13:35:33 EDT 2021
Thank you.
“One of the things I have found with LA batteries at high charge rates causes shortened battery life. Check with Harris for the maximum charge rate. “
I had another opinion very similar to yours and had just reached out to Harris for this info. Will keep you all informed.
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Darryl Thayer
Sent: Thursday, November 4, 2021 12:26 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Harris lithium battery as drop-in replacement for Outback RE2200 AGM?
forgive me I am not the brightest bulb. But if you are replacing the Outback 2200 RE with 2100 AH and about 1100 AH usable, or @ 51V then 56 kWh with Lithium, 62 kWh, Do you have the charging capacity to charge at 280 amps? This is to allow full use of the solar array. One of the things I have found with LA batteries at high charge rates causes shortened battery life. Check with Harris for the maximum charge rate. You will be charging two in parallel the battery BMS will have to handle the BMS in each battery. Also, check the top balance current of the batteries to assure the low cells can be balanced in the perhaps 4 hours. The charge controllers will limit on voltage and the batteries will be in top balance current, is this ok with Harris? You will use multiple charge controllers, I try to set the voltages a little lower on two of the charge controllers to create a tapered charge.
On Thu, Nov 4, 2021 at 10:50 AM <scot.arey at solarcentex.com <mailto:scot.arey at solarcentex.com> > wrote:
Does anybody have insight as to the Harris lithium battery and its use as a replacement for a RE2200 AGM that needs replacement?
Our setup is dual Radian 8048s for a full off-grid home with 14KW of solar. System has performed fine but the AGMs are not doing well holding charge and customer is ready to move to lithium.
For those with background, did you use the multi-battery controller? Was the Mate and its BMS capability sufficient for lithium use?
Here is the battery we are planning on and will use two of these : RELi48-31.0 - Harris Battery - Industrial <https://www.harrisbattery.com/product/reli48-31-0/> & Commercial Battery Supplier
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211104/306ef4c0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 27572 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211104/306ef4c0/attachment.png>
More information about the RE-Wrenches
mailing list